Re: Help ry100fj7v1
So you have 30 degrees C coil temp but also 30 degrees C air off the indoor unit?
As Frank says more pressure/temps are required to help with the diagnosis.
Suggest
Discharge pressure or liquid pressure (SCT)
Discharge temperature after the compressor
Liquid temperature
Suction temperature
Suction pressure (SST)
Air on/off indoor
Air on/off outdoor
You need to see if the discharge temperature from the compressor is much higher than your indoor coil temp, if it is then start with looking at the 4 way reversing valve.
If its not then start looking at low superheat flooding the compressor which will affect the discharge temperatures.
Again without knowing the temps & pressures its just guessingThe difference between genius and stupidity is that genius has its limits.