    Carrier 30RQ EXV problem



    Hi All. I have 30RQ120 Chiller with AquaSnap Control System.
    In cooling mode, the unit is working fine.
    In the heat pump:
    The unit starts up and gets into position EXV 27% and off for high pressure
    EXV on the sensor does not respond - only 27%
    I heated the sensor - no reaction - 27% and off for high pressure
    In what could be the reason?
    Thanks in advance for your help



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Carrier 30RQ EXV problem

    Maximum and minimum temperatures
    Cooling mode
    Water heat exchanger (evaporator) Minimum Maximum
    Entering water temperature at start-up °C 6.8 30
    Leaving water temperature during operation °C 5 15
    Entering water temperature at shut-down °C - 60
    Air heat exchanger (condenser)**
    Air entering temperature °C 0 46
    Heating mode
    Water heat exchanger (condenser) Minimum Maximum
    Entering water temperature at start-up °C 8* 45
    Leaving water temperature during operation °C 20 50
    Entering water temperature at shut-down °C 3 60
    Air heat exchanger (evaporator)
    Air entering temperature** °C -10 35
    Last edited by Brian_UK; 06-01-2013 at 10:20 PM. Reason: text resized

  3. #3
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    24

    Re: Carrier 30RQ EXV problem

    A bit more information would help, does it trip in heat or defrost mode. Can you supply a running log of what the unit is doing when it trips.