    Lennox lch 853/953 anyone??



    Hi peeps, I was just wondering if anyone has a fault list for a lennox chiller with a kp02 controller. I can't get any info anywhere and lennox technical are ok, but dont have the info.

    I have a lch 853 with a 117 code and a 953 with a 37 and 12 code.

    Any help or technical info would be appreciated.

    I do have variable list for both these chillers, but only up too 100 and I cant change them as I dont have password.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox lch 853/953 anyone??

    117 low pressure circuit 1 password to access higher level is 63 http://www.mediafire.com/view/?b8oek64tt4cahto chiller manual Contact name: Dave Lyons
    Tel: +44 7713 792 029
    Fax: +44 1604 669150
    Email: Dave.lyons@lennoxeurope.com

  3. #3
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    43
    Posts
    62
    Rep Power
    17

    Re: Lennox lch 853/953 anyone??

    Oh thank you much appreciated

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox lch 853/953 anyone??

    lennox website has changed- used to be able to get all sorts of manuals- now nothing

  5. #5
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    43
    Posts
    62
    Rep Power
    17

    Re: Lennox lch 853/953 anyone??

    The website site is rubbish, I had to change a kp07 controller to an kp02 and there technical department wouldn't tell me much about it. I kept getting a pb con fault on kp02, in the end I worked out i had to flick a dip switch on the kp01 to activate the controller.

    They was happy to send me and engineer though.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox lch 853/953 anyone??

    yep lennox are quite happy to send u an engineer- for about 400quid a day- the northern engineer lives in Huddersfield , your lucky to get 6hrs out of him!! and to get a price for parts you have to email Europe, they wont answer the phone- and after 3weeks of waiting for parts you open the box to find they sent ya the wrong bit!

  7. #7
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    43
    Posts
    62
    Rep Power
    17

    Re: Lennox lch 853/953 anyone??

    He lives near me then. £400 a day is a bit steep.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox lch 853/953 anyone??

    if you know where he lives- invite yourself for coffee,biscuits and manual share
    Quote Originally Posted by W.Miller View Post
    He lives near me then. £400 a day is a bit steep.

  9. #9
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    43
    Posts
    62
    Rep Power
    17

    Re: Lennox lch 853/953 anyone??

    I think the 12 fault is suction temperature probe and according to the kp02 controller variable 71 is on (expansion opening fault circuit 3) so that maybe the 37 fault.

    Can I correct a mistake as its a lch 984 not 953

  10. #10
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    43
    Posts
    62
    Rep Power
    17

    Re: Lennox lch 853/953 anyone??

    117(or mn7 in the manual) is internal protection, i have a faulty motor protection unit (proven today). To be fair the lennox guy did tell me but i was confused by the mn which m= circuit and n= compressor

    Hope this helps any future reader.