    Daikin h3p



    Split system r410a, 2007.

    Any one know where I can find list of faults / descriptions for the outdoor yellow led's.

    Also how to force run the system from outdoor... As I don't have access to the hard wire controllers due to locations & time restrictions.



  2. #2
    Join Date
    May 2010
    Location
    W.Yorkshire
    Posts
    31
    Rep Power
    0
    Quote Originally Posted by Aircon467 View Post
    Split system r410a, 2007.

    Any one know where I can find list of faults / descriptions for the outdoor yellow led's.

    Also how to force run the system from outdoor... As I don't have access to the hard wire controllers due to locations & time restrictions.
    Ps thanks In Advance.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    normally on inside of the cover on the outdoor- but theyre usually general, system safety device- u need to interogate the indoor controller to define the problem

  4. #4
    Join Date
    May 2010
    Location
    W.Yorkshire
    Posts
    31
    Rep Power
    0
    The indoor controller is blank. But... It's 1 common controller attached to 4 splits... Only 1 of the splits is working.... Other 3 have desperate probs.... All of which the controller is blank. Unless the one system that works is powered on.

  5. #5
    Join Date
    May 2010
    Location
    W.Yorkshire
    Posts
    31
    Rep Power
    0
    Quote Originally Posted by Aircon467 View Post
    The indoor controller is blank. But... It's 1 common controller attached to 4 splits... Only 1 of the splits is working.... Other 3 have desperate probs.... All of which the controller is blank. Unless the one system that works is powered on.
    **^^^separate... Not desperate .. Lol

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Daikin h3p

    If it's been wired correctly (4 x indoors to 1 x controller) then the working indoor unit should power the remote controller.

    Daikin outdoor units don't have yellow leds for fault codes.

    Use the advanced Search Button at the top of the screen for 'Daikin Fault Codes'

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    is it a multi split 4mx type with 4 lots of pipework to the outdoor or single split with 4 indoors- 1 common piperun? give us the outdoor model number.
    Quote Originally Posted by Aircon467 View Post
    The indoor controller is blank. But... It's 1 common controller attached to 4 splits... Only 1 of the splits is working.... Other 3 have desperate probs.... All of which the controller is blank. Unless the one system that works is powered on.

  8. #8
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin h3p

    i have a 4mx in my house.....It has an absolute mind of it's own, bit like an alfa romeo but not as cool.

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    have you designated the master indoor unit, they are problematic with outdoor lev's passing,sticking.

  10. #10
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin h3p

    Quote Originally Posted by install monkey View Post
    have you designated the master indoor unit,
    Yehh did this when i installed it. Now, if my daughter has hers in heating all the house is in heating. Switched on or not.....
    if I put mine in cooling, i get about 5k across the cassette, unless I switch on one in another room, then we all get 11k. If I put mine in heating, I get about 10k.........unless I switch on another.....then we get 20k..

    Like i say, it's like an alfa romeo. We don't try to make sense of it, it just does what we ask....if we ask it in the right way. Romance it a little, learn how she works.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    have you checked the gas charge? have you regularly serviced it, and cleaned the coils, inc outdoor with nitrogen-check indoor coils for corrosion from incorrectly mixed evap coil cleaner.
    do you want a service manual??

    Quote Originally Posted by eggs View Post
    Yehh did this when i installed it. Now, if my daughter has hers in heating all the house is in heating. Switched on or not.....
    if I put mine in cooling, i get about 5k across the cassette, unless I switch on one in another room, then we all get 11k. If I put mine in heating, I get about 10k.........unless I switch on another.....then we get 20k..

    Like i say, it's like an alfa romeo. We don't try to make sense of it, it just does what we ask....if we ask it in the right way. Romance it a little, learn how she works.

  12. #12
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin h3p

    Quote Originally Posted by install monkey View Post
    have you checked the gas charge?
    Have i F$$$

    Quote Originally Posted by install monkey View Post
    have you regularly serviced it, and cleaned the coils, inc outdoor with nitrogen-check indoor coils for corrosion from incorrectly mixed evap coil cleaner.
    Behave your self..

    Quote Originally Posted by install monkey View Post
    do you want a service manual??
    NO !!!! not ever.

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    tayters offers a 24 hr inverter check , and he does it for a small donation- if you cant be bothered to check it- pretty sure the mx units hold 3.5kg of gas and are legible for annual leak checks! haha
    Quote Originally Posted by eggs View Post
    Have i F$$$



    Behave your self..



    NO !!!! not ever.

  14. #14
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin h3p

    Quote Originally Posted by install monkey View Post
    tayters offers a 24 hr inverter check , and he does it for a small donation- if you cant be bothered to check it- pretty sure the mx units hold 3.5kg of gas and are legible for annual leak checks! haha

    Yehhhhh, I'm an anarchist. F the system. i'm a ducter and I bought the system of e-bay with a self install kit. What they gonna do about it? ......and I didn't have my part p at the time either

    Eggs

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    maybe you should have done a 24 hr plumbing course! haha
    Quote Originally Posted by eggs View Post
    Yehhhhh, I'm an anarchist. F the system. i'm a ducter and I bought the system of e-bay with a self install kit. What they gonna do about it? ......and I didn't have my part p at the time either

    Eggs

  16. #16
    Join Date
    May 2010
    Location
    W.Yorkshire
    Posts
    31
    Rep Power
    0
    Rzqs125c7v1b ... 4 single splits aprox 6 year old

    3 not working 1 fine.

    Had a couple of hours on it today and got it bottomed...

    The one with h3p light on o/c unit - turned out 1 wire had been pulled from the p1/p2 control connection,

    Another one had a faulty compressor -

    Another one had faulty indoor pcb.


    Simples...... Can't belive how bad condition they were to say they have a maintenance team on site 1 day a week. ?!?!?!

  17. #17
    Join Date
    May 2010
    Location
    W.Yorkshire
    Posts
    31
    Rep Power
    0
    Quote Originally Posted by eggs View Post

    Yehhhhh, I'm an anarchist. F the system. i'm a ducter and I bought the system of e-bay with a self install kit. What they gonna do about it? ......and I didn't have my part p at the time either

    Eggs
    Lmfao !! U go lad !

  18. #18
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin h3p

    usually maintenance teams start off on site ontop of all defects and maintenance, then a few years down the line they are tea conisseurs and usually have a stash of chuff mags in the plantroom and a comfy chair

    Quote Originally Posted by Aircon467 View Post
    Rzqs125c7v1b ... 4 single splits aprox 6 year old

    3 not working 1 fine.

    Had a couple of hours on it today and got it bottomed...

    The one with h3p light on o/c unit - turned out 1 wire had been pulled from the p1/p2 control connection,

    Another one had a faulty compressor -

    Another one had faulty indoor pcb.


    Simples...... Can't belive how bad condition they were to say they have a maintenance team on site 1 day a week. ?!?!?!