    Toshiba R407c Reversing Valves



    I've been coming across Tosh RAV heat pumps running on R407c where the reversing valve has either stuck or is getting sticky.

    The units have probably been working more on cooling than heating of late but ...

    Has anyone else had similar problems ?


    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Toshiba R407c Reversing Valves

    If you are talking about Tosh single splits, the reversing valve is a fairly robust device and it takes a fair amount to put it out of action.

    Apart from a dud valve ? Tosh buy them in from Saginomiya, Ranco, and other valve OEMs as do most of the other Japanese manufacturers ? the reversing valves need at least 5 or 6 bar pressure differential to move the piston or internal chariot. Unless there?s a chunk of debris in there they tend to either work or not work. After all it has only one moving part.

    But Tosh units have some peculiarities that may impact on the way the valve can work efficiently and not be immediately apparent. There is an unmarked filter in the system.

    1. First, the compressor isn?t pumping. Obvious, I know, but it happens. I?m sure you?ve checked this because the pressures won?t be right. Some of the larger OD units have a schrader stub on the main suction return from the valve to the comp. It gives true suction pressure all the time, whereas the service valve port gives discharge pressure in heating.

    2. The second gives the impression of a compressor not pumping and is unique to Tosh as far as I know. There is a small wire gauze filter in the suction pipe entry to the accumulator. It?s exceptionally difficult to see because it is in the pipe, covered in insulation and there are no marks to indicate its presence. The pipe at this point is ?? OD, so it?s small. It?s located about 70mm up the pipe on the entry side. If this blocks, the compressor gives the impression of not pumping or partial pumping. If pipes are shoved through walls uncapped, for example, this is the first place that masonry debris will collect. The pressures on the suction service valve and the suction stub will show a pressure loss across the filter if this is the case.

    3. A third instance also involved the suction filter. Contaminated oil waxes up in the gauze makes a restriction and the resulting freeze solidifies more oil and blocks it. As soon as the temperature at this point rises, it dispersed and the unit worked until the next time. It happened intermittently in cooling. It?s very rare, but it does happen.

    Frankly, that filter was a menace.

    Hope this helps.

    .
    ________
    medical marijuana news
    Last edited by Argus; 07-02-2011 at 08:24 AM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Toshiba R407c Reversing Valves

    Noted, thanks Argus
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Replies: 19
    Last Post: 18-10-2010, 02:45 PM
  2. Stainless steel valves
    By Tycho in forum NH3
    Replies: 5
    Last Post: 05-11-2008, 02:16 PM
  3. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Replies: 6
    Last Post: 14-04-2008, 01:47 AM
  4. Suction Stop Valves
    By frank in forum Air Conditioning
    Replies: 10
    Last Post: 02-08-2006, 11:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •