Results 1 to 10 of 10
    Robert88's Avatar
    Robert88 Guest
    Maneurop Compressor shaking on start up
    Has anyone had problems with new single phase maneurop compressors (MTZ28). I have had a few that shake on start up and pull around 44amps before either starting or blowing the circuit breaker or the capacitor. At other times the same compressor has started with no problems. Not sure what to do other than change the brand of compressor which then works fine on the system. Any easy solution???
    Jun 2009
    Lusk , Dublin
    1,115
    Re: Maneurop Compressor shaking on start up
    Flooding in off cycle. crankcase heater duff or if part of a tandem or multiple no nrv on discharge.
    Or maybe none of the above, but it's obviously strugling to get away,could be jumping the springs but would expect it every time.
    Stu
    Jul 2010
    u.k
    82
    8
    How are the electrics, relay, caps etc,might be worth putting new on.
    Quote Originally Posted by stufus View Post
    Stu
    Mar 2010
    usa
    120
    Im assuming the Voltage and start componets are good. Will it start with the Suction and Discharge pressures Equalized?
    Robert88's Avatar
    Robert88 Guest
    Does the same when the pressures are equallised. It is running off a 2.5mm lead with a 10amp plug. Do you think this could cause the problem?
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    What is the length of your 2.5mm lead?
    What is the compressor running amps...as stated on it's specifications label.
    Use a Fluke, or similar meter to do a minimum/ maximum voltage logging to see what the volts drops to during start up.
    Mar 2008
    232
    Quote Originally Posted by Robert88 View Post
    Is this a new installation or a retro-fit?
    Location, United Kingdom
    Robert88's Avatar
    Robert88 Guest
    Quote Originally Posted by B G Scott View Post
    It is a retro-fit
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    Suspect low voltage on start up...Had a chance to do that minimum voltage test yet? (Post #6)
    Mar 2008
    232
    It is a retro-fit
    First check that the compressor is operating within the design parameters as set out in the selection data provided by the manufacturer.
    As this is already fitted put your amp probe on the supply cable, wind in the suction service valve and start the unit, observe the current drawn and slowly open up the suction service valve and see if you get a smooth start and a current draw in line with the published data.
    If you do consider installing a crank case protection valve in the suction line to limit the suction pressure during pull down to within the limits as detailed in the data sheet.
    When installed check the current drawn on start up and set the valve opening to keep the amps within the tolerance levels indicated by the data sheet.