Re: COP and Superheat - does is it help?
But in coolpack, you should split the superheat between useful and non useful. So in your example you can only have 1K useful and 2K non useful. (increasing to 7K non useful)
So increase the system superheat, then you must say it is the non useful superheat that has to increase. (exclude the S/L heat exchanger)