Thread: daikin cassette FXFQ-M8V3B
-
14-09-2012, 02:35 PM #1
daikin cassette FXFQ-M8V3B
dear all.
I has been problem with daikin cassette FXFQ-M8V3B it give A3 .
can any person help me ؟
Thanks .
-
14-09-2012, 04:03 PM #2
Re: daikin cassette FXFQ-M8V3B
A3 Indoor Malfunction of drain Level control system
you got a problem with the drain. The pump is running too long and the float isn't dropping down within time..
-
15-09-2012, 09:00 AM #3
Re: daikin cassette FXFQ-M8V3B
yes, the pump is always running ,
what should i do to solve that problem ?
thanks
-
15-09-2012, 11:03 AM #4
Re: daikin cassette FXFQ-M8V3B
call an engineer?
-
15-09-2012, 11:38 AM #5
Re: daikin cassette FXFQ-M8V3B
youve got faulty floating switch,sensor etc......
-
15-09-2012, 04:32 PM #6
Re: daikin cassette FXFQ-M8V3B
cassette lift pumps on daikins run constantly when in cooling mode and for 1 minute afterwards, either slime /crap in ur drip tray or the drain off the unit is blocked- on the outside of the cassette remove the jubilee clip on the drain - see if it pumps into a bucket, then if this is ok, blow down the drain pipe you disconnected- it may be healthier using compressed air butit gives you a few pointers to check, if the drain is clear and the condensate pump shifts water then the hi lmit float switch may be stuck/jammed- or as a last resort unplug the float plug off the pcb, in uk its a yellow 2 core wire, test continuity on the plug- i have had a float switch fail when all is ok.
-
16-09-2012, 12:23 PM #7
Re: daikin cassette FXFQ-M8V3B
Check condensate pump and flow switch !!!!
-
16-09-2012, 07:06 PM #8
-
16-09-2012, 08:09 PM #9
Re: daikin cassette FXFQ-M8V3B
I bet it's been many moons since the drain pan was removed and cleaned
-
22-09-2012, 09:20 AM #10
Re: daikin cassette FXFQ-M8V3B
Thanks to all .
the problem in drain pipe is closed .
we found snake in it .
-
22-09-2012, 09:23 AM #11
Re: daikin cassette FXFQ-M8V3B
U jooking !!!!loooooooooooooool