    Exclamation Mc Quay mng 168.2 se st screw. loading/unloading settings
    Hi gents .
    Back again
    Looking for the settings as per above as the settings in the manuall i have are not doing what they should
    no. load pulses - 6
    no. unload pulses -9
    loading..
    pulse time 0.2s
    min pulse period 30s
    max pulse period 150s
    unloading
    pulse time 0.4s
    min pulse period 1s
    first pulse timing
    loading 1s
    unloading 0.8s
    Can anyone verify or correct these figures as these issues are causing a major fooking head ache.
    cheers
    Stu
    manchester
    5,639
    Re: Mc Quay mng 168.2 se st screw. loading/unloading settings
    where did u get the manual from?- ive searched through mcquays site,trolling for manuals for me paddy mate and no joy!- are u dragging that job out for a bit of overtime?- things you do to stay away from squarking kids
    Jun 2009
    Lusk , Dublin
    1,115
    The manual is the one that came with the chiller.
    There's two of these on the site two circuit's each chiller, one of the compressors was replaced and this loading issue was spotted by one of the lads i work with.
    We had a mooch around the other three circuits and they all have loading/unloading issues.
    And as per usual McQuay aren't being very forthcoming with a straight fookin answer.
    Stu
    manchester
    5,639
    could you scan it and upload it for us, not that i know anything about mcquays, just for storing on me hard drive, as toilet literature
    Jun 2009
    Lusk , Dublin
    1,115
    No chance.
    Dec 2009
    New zealand
    22
    Sorry just was going through some other Mcquay stuff and read your thread, hope you already found your settings but from seeing from the settings above they are wrong thus issues with loading and unloading. let me know if you still need help.
    Jun 2009
    Lusk , Dublin
    1,115
    They are the commissioning settings as provided and set by McQuay.
    Had them back to site and they said it was fine, bollox to that it's still not running correctly.
    What setting's would you recommend??
    Stu
    Jun 2012
    Germany
    4
    Hi Stu,
    have a look at the attached file.
    The most important thing is to use a current clamp to adjust and check the pulse time settings.
    Hope this helps.
    Attached Files Attached Files
    Jul 2008
    GREECE
    Your settings are o.k. Where is your problem ?