adding a cassette to a chilled water system.
Hi all.
For the above am I correct in assuming that it is just a case of chopping into the existing water circuit, fitting a couple of gate valves and then bunging in the cassete with a chilled water valve?
It is a small retail store within a large shopping centre that has a landlords chiller connection for flow and return. Surely it can't be that simple, what am i missing?
Cheers
Eggs
-
10-08-2012, 06:09 PM #2
Re: adding a cassette to a chilled water system.
Yep, it should be that simple.
Probably worth while a including a balancing valve especially if there are any other units in there or more to be added later. It will also give you a means of proving that the landlord is providing the required water flow if any argument should arise about performance.
Don't forget the pipe insulation... sometimes worth adding a small drip tray underneath the valve set close to the unit to catch the errant drips.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
10-08-2012, 06:15 PM #3
Re: adding a cassette to a chilled water system.
Thanks Brian.
Please excuse my ignorance, where would the balance valve be installed at the inlet to the cassette or onto the landlords inlet?
Cheers
-
10-08-2012, 07:12 PM #4
Re: adding a cassette to a chilled water system.
fit the regulating (balancing) valve on the chilled water return pipe, you can get comissioning sets from pipeline ctr if the manufacturer of the unit doesnt supply them, ideally you need to check flowrates through the system as adding an additional cassette will affect flow rates to the other units,-good luck
-
10-08-2012, 07:29 PM #5
Re: adding a cassette to a chilled water system.
You are right,
In theory it is dead simple, however...
Having done similar things in a few shopping centres up and down the country, in my experience it is a minefield.
Your best bet is to ask (or get the shop owner/manager to) the centre management people what they expect and will allow before any design and pricing up is done.
In some centres it is simple, 2 flow controlled pipes enters each unit and the individual shop can do whatever they like with it within their walls.
From there it will escalate...
The worst one was where the centre management specified specific energy monitoring units to be fitted by their contractors (@ a rate of £900/day), specified the brand of the fan coils and even what type of fittings and lagging that must be used...
Good luck,
.
-
10-08-2012, 10:11 PM #6
Re: adding a cassette to a chilled water system.
Thanks for the input chaps, it's given me some food for thought.
Cheers
-
11-08-2012, 11:37 PM #7
Re: adding a cassette to a chilled water system.
Make sure it's not a dry cooler loop for water cooled systems before connecting.
Have seen it done more than once!!
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
12-08-2012, 01:27 PM #8
Re: adding a cassette to a chilled water system.
Now that would be opening up a can of worms ....think I best visit site.
Cheers
-
12-08-2012, 09:55 PM #9
Re: adding a cassette to a chilled water system.
Not to mention any names Stufus, but would that be in a shopping centre that rhymes with bundrum?
@eggs definitely visit site! Ask for the landlords connection handbook, they may have specific requirements for connection arrangements and also for working arrangements (ie no drilling or hammering or hot works or cutting or breathing between 1am and midnight when there is a y in the day which you won't get paid for afterwards).
-
13-08-2012, 08:44 PM #10
-
13-08-2012, 08:55 PM #11
Re: adding a cassette to a chilled water system.
heat reclaim!! - mcr arndale have a condenser water loop, ur limited to about 80kw of cooling per retail outlet, any extra req consultants,meetings and plans- i would like to apologise for ripping out 2x 10kw units and sticking in 2x 15kw units- it was lennoxs fault,and in my defense theres a unit downstairs with no gas in so i havent exceeded the maximum capacity
-
29-08-2012, 04:50 PM #12
Re: adding a cassette to a chilled water system.
The plot thickens....and the job grows....
Can I please have a bit more help?
The landlord provides chilled water and the primary pumps are sized to 40kPa per retail unit. When I add all my figures up I require 1.008 l/s of water and my kit pressure drop is 60.6kPa not including pipe work.
Is this where shunt pumps are needed?
Cheers
Eggs
-
29-08-2012, 05:27 PM #13
Re: adding a cassette to a chilled water system.
Second thoughts..
Can anyone recommend a design engineer to do the business??
Cheers
Eggs