    compressor burn out



    What causes compressor burn out?
    Is it just moisture/acid? Does a burn out cause acid to be left behind?

    Got a package a/c that's 10 years old with the compressor shorted to earth.
    I can't see moisture acid causing the burn out since it's a package a/c so factory piping and charging, so no field piping/evac or refrigerant charging done. Plus also it's age, I can't see it lasting so long with moisture/acid in the system.

    I want to know what could be the cause so there's no problem with the replacement compressor as it's a $3k compressor.
    Last edited by Dunno_Daikin; 22-08-2012 at 04:30 AM.



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: compressor burn out

    Many causes out there for compressors to burn out. Power supply problems like a surge or brown-outs, contactor failure, compressor overheating from clogged condenser, refrigerant breakdown or just wear and tear.
    Have to flush system before installing new compressor and weld in a suction line drier for added protection.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: compressor burn out

    The fact it ran for ten years indicates the design appears OK. The important thing for the new $3K compressor is that the system is cleaned to acceptable standards & as Mike said -drier, filter + new start gear. Just again the system must be proved to be clean, use an acid test kit & search forum for procedure if necessary.

  4. #4
    Join Date
    Jul 2012
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: compressor burn out

    I used an emerson acid test kit on the current compressor oil and it tests OK?

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: compressor burn out

    The phrase "burned compressor" boils down to failed windings insulation.
    Windings insulation failure is caused by high temperature/acidity,etc.
    Acidity already having been discussed, high temperature is caused by high current /high pressure, etc, .

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: compressor burn out

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    26

    Re: compressor burn out

    Not much use in Australia , considering you are in Seattle WA.....
    Now we have cleared that up , Stop advertising!!!!!!
    Cheers
    Stu
    Quote Originally Posted by makrin View Post
    I strongly recommend securecomfort. As they provide the best service for your air conditioning system and ensure a permant fix to the problem.
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •