    Need help with r404 chiller diagnostics



    Hi.Was called out to a counter chiller unit today useing r404.The unit at first glance seemed to be working but when the lid is opened,the temperature creaps up...Tried blowing out condensor coils but made no difference..Any suggestions extremely welcome.First post ever made

    Rob



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Need help with r404 chiller diagnostics

    Pressures OK?
    Subcooling OK?
    Superheat OK?
    The temp of the air entering the condensor?



    .

  3. #3
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: Need help with r404 chiller diagnostics

    Hi

    If you close lid does it run fine again?
    Just asking because it might take all air through the lid ,not through the condenser.
    i need more specs for the machine you`re about to fix for better answers.