Thread: dryer fault
-
05-08-2012, 03:35 PM #1
dryer fault
Hi,
Got a integral dryer on atlas copco air compressor,fault is dewpoint high at 17 degrees should be about 3. when gauges on high side 16 bar with fan coming in, low side showing 10 bar.hbpv on this system and does nothing when ajusting,any advice what might be fault.r404 gas 3.9kg
cheers
-
05-08-2012, 03:48 PM #2
Re: dryer fault
low side pressure is high comp pos not pumping corectly or hot gas bypass valve stuck open
-
05-08-2012, 04:08 PM #3
Re: dryer fault
I`ll go with martin on this, looks like the hot gas valve is stuck open. Try giving it a few taps with a toffee hammer to see if it frees the valve up. Just support the opposite side to support it
-
05-08-2012, 05:12 PM #4
Re: dryer fault
Thanks for reply guys ,will try looking at hbpv again or replacing. thanks again
-
05-08-2012, 07:46 PM #5
Re: dryer fault
replace the refrigerant. its a common problem on atlas copco driers.