    dryer fault



    Hi,
    Got a integral dryer on atlas copco air compressor,fault is dewpoint high at 17 degrees should be about 3. when gauges on high side 16 bar with fan coming in, low side showing 10 bar.hbpv on this system and does nothing when ajusting,any advice what might be fault.r404 gas 3.9kg

    cheers



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    503
    Rep Power
    21

    Re: dryer fault

    low side pressure is high comp pos not pumping corectly or hot gas bypass valve stuck open

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: dryer fault

    I`ll go with martin on this, looks like the hot gas valve is stuck open. Try giving it a few taps with a toffee hammer to see if it frees the valve up. Just support the opposite side to support it

  4. #4
    Join Date
    Sep 2010
    Location
    manchester
    Age
    52
    Posts
    47
    Rep Power
    0

    Re: dryer fault

    Thanks for reply guys ,will try looking at hbpv again or replacing. thanks again

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: dryer fault

    replace the refrigerant. its a common problem on atlas copco driers.