    ME Mr. Slim MS-A30ND



    Hi!

    I've been browsing the old posts hoping to see threads similar to my problem, finding none, I decided to post this. I will try to explain the problem to the best of my knowledge and please bear with me. Here it goes...

    Brand: Mitsubishi Electric
    Model: Mr. Slim model MS-A30ND

    Problem Encountered:

    The compressor draws too high current during start-up then stops (current drop to zero) after 5-10 seconds. The standing pressure measured on the gas line from the indoor unit is around 150-psig. During the start-up phase, this pressure remains the same (the compound gauge is in good condition).

    I checked the winding resistances and the values looks good in fact they are the same compared to other working units. I tried swapping some components e.g. capacitor and control board with the other units but the problem is still the same.

    Could this be a problem of stuck compressor? If yes, what course of action would you recommend?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: ME Mr. Slim MS-A30ND

    inspect the compressor terminals on the compressor,if ok ie all 3 leads connected then compressor siezed- best get a new system for warranty reasons-as replace the compressor and then something else will fail

  3. #3
    upul45's Avatar
    upul45 Guest

    Re: ME Mr. Slim MS-A30ND

    Check operation of LEV .it is open or no

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    502
    Rep Power
    21

    Re: ME Mr. Slim MS-A30ND

    sounds like a siezed compressor