Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2007
    Location
    Iraq
    Posts
    44
    Rep Power
    0

    McQuay centrifugal chiller



    Hello friends

    I have a problem in McQuay centrifugal chiller Model WSC 079 when starting the chiller the oil pump run and shows low net pressure , the oil migrates to the condenser and oil level drops , when adding excess oil the same phenomena is repeated and more oil is lost , please tell me the reason for this case .
    so many thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: McQuay centrifugal chiller

    How far does the level drop?

    How long ar you running the machine for?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2007
    Location
    Iraq
    Posts
    44
    Rep Power
    0

    Re: McQuay centrifugal chiller

    Dear Sir :

    thanks for your early reply, the level drops for about two liters for period of 30 sec at pre-lubrication then micro tech display shows vane open and the chiller shut down

  4. #4
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: McQuay centrifugal chiller

    Please list oil temperature, oil pressure and evap pressure just for starters. what is your starting oil level? is it visible in the glass?

  5. #5
    Join Date
    Mar 2008
    Location
    Glasgow
    Posts
    5
    Rep Power
    0

    Re: McQuay centrifugal chiller

    Hi Do you have a separator with in the system?

  6. #6
    Join Date
    Jul 2007
    Location
    Iraq
    Posts
    44
    Rep Power
    0

    Re: McQuay centrifugal chiller

    Dear friends

    thanks for your interest the oil temp is (47 oC) , oil net pressure = 5 bar at beginning of oil pump starting then quickly drops to 1.5 bar and oil level disappears from sight glass , before oil pump operation the oil level is normal , I added oil to the sump three times to recover the normal level but the same problem was repeated

  7. #7
    Join Date
    Jul 2007
    Location
    Iraq
    Posts
    44
    Rep Power
    0

    Re: McQuay centrifugal chiller

    Dear friend
    there is no oil seperator within the system

  8. #8
    kleen's Avatar
    kleen Guest

    Re: McQuay centrifugal chiller

    look like a oil leak in vane inlet maybe a torn o ring

  9. #9
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: McQuay centrifugal chiller

    Khaled hilaly the cause of your problem is oring or orings within the igv have failed which will cause loss of oil return to pot and oil pressure this is a common problem with all mc quay centrifugal chillers I have the oil problem bulletin + check procedure to diagnose fault send me your email address