Thread: McQuay centrifugal chiller
19-04-2012, 06:57 PM #1
Hello friends
I have a problem in McQuay centrifugal chiller Model WSC 079 when starting the chiller the oil pump run and shows low net pressure , the oil migrates to the condenser and oil level drops , when adding excess oil the same phenomena is repeated and more oil is lost , please tell me the reason for this case .
so many thanks
19-04-2012, 11:29 PM #2
Re: McQuay centrifugal chiller
How far does the level drop?
How long ar you running the machine for?Brian - Newton Abbot, Devon, UK
20-04-2012, 06:53 AM #3
Dear Sir :
thanks for your early reply, the level drops for about two liters for period of 30 sec at pre-lubrication then micro tech display shows vane open and the chiller shut down
20-04-2012, 08:49 AM #4
Please list oil temperature, oil pressure and evap pressure just for starters. what is your starting oil level? is it visible in the glass?
20-04-2012, 12:07 PM #5
Hi Do you have a separator with in the system?
20-04-2012, 12:24 PM #6
Dear friends
thanks for your interest the oil temp is (47 oC) , oil net pressure = 5 bar at beginning of oil pump starting then quickly drops to 1.5 bar and oil level disappears from sight glass , before oil pump operation the oil level is normal , I added oil to the sump three times to recover the normal level but the same problem was repeated
20-04-2012, 12:27 PM #7
Dear friend
there is no oil seperator within the system
17-05-2012, 03:25 AM #8
look like a oil leak in vane inlet maybe a torn o ring
14-07-2012, 03:32 AM #9
Khaled hilaly the cause of your problem is oring or orings within the igv have failed which will cause loss of oil return to pot and oil pressure this is a common problem with all mc quay centrifugal chillers I have the oil problem bulletin + check procedure to diagnose fault send me your email address