Results 1 to 22 of 22
    Jul 2002
    Derby
    22
    High superheat but major frosting on compressor
    I have a system which is showing a low suction pressure ( -32 deg c sat )
    And a high super heat of 20 deg c
    But the compressor is showing major frosting as if liquid flood back and even Sticky to touch , temp at compressor inlet 8 deg c
    The evap coil isn't showing any real signs of frosting and the controlled space at -10 deg c and air On off Td is low
    There seems to be a lot of oil carried in the system , system is R422d
    I'm just confused as to why so much frosting at this temp ?
    Any help or advise welcome
    Jun 2009
    North East England
    712
    Re: High superheat but major frosting on compressor
    Sounds like its low in refrigerant in theory you shouldn't have frost where liquid is present Low td also
    the same as is high superheat
    3,363
    kfjoe,
    It has been said numerous times in other post, do you have a liquid/suction line heat exchanger
    that could be internally fractured?
    Some heat exchangers are obvious, while others are built in fan casing of evaporator.
    Measure superheat at evaporator bulb to see if its same as compressor, if not its something downstream of TX bulb.
    Jul 2002
    Derby
    22
    No heat exchanger , superheat at bulb 20 and at compressor 18
    It's just the amount of frost and how rapid on compressor that I find strange
    Dec 2010
    ireland
    replace exspansion valve and check the size orofice.... or someone might have screwed open the valve to the last... maybe try adjusting valve to get proper superheat in coil
    Is the compressor surface temperature below the ambient dew point?
    Jul 2002
    Derby
    22
    Yes it's at -8 , so I understand it will frost
    It's just the amount of frosting and the sticky to touch as if it's liquid
    As there seems to be a lot of oil around the system , I'm wondering if this has some bearing on readings etc
    Feb 2012
    Bolivia
    270
    14
    1) Maybe you should measure superheat at hours of low thermal load. The system could be hunting then.
    2) Check your oil separator, it could be condensing significant amounts of refrigerant. You'll see foaming when the float opens.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!
    Jul 2010
    manchester
    212
    what is your suction pressure?
    what is your discharge pressure?
    i would suspect also that if the system is on R422d and it is a low temp aplication it should have liquid injection?
    is the liquid injection control faulty hence too much liquid in the suction.
    your only as good as your last job
    Oct 2008
    newbury
    1,444
    Quote Originally Posted by cold.man View Post
    You could be onto something here.. starved system = high superheat=high discharge temp = liq injection...
    Nov 2005
    belgium
    61
    compressor to strong for the evaporator
    Jul 2002
    Derby
    22
    Thanks for all the replies guys
    The superheat isn't as high as I thought , it's 11 deg c
    Liquid injection is fine
    I have a poor TD across the coil and a low evaporating temperature but airflow is good
    No oil separator on this system
    There is a lot of oil in the system though and you see this when taking off the low side gauge line
    I'm wondering if the oil is effecting the evaporator and giving it its poor TD ?
    3,853
    What oil is it running on? POE or mineral? POE would be better with R422D.
    What was fault you were called to fix?
    Has the system ever worked since being converted to R422D?
    Jul 2010
    manchester
    212
    as monkey spanners said POE is better with R422d
    If the system has been retrofitted from R22 and was on mineral oil change the oil to POE or at least a 80% POE 20% mineral oil mix if the compressor is still the same.
    oil return with minerial oil on R422d is poor, does the system have an oil saftey switch?
    What set up do you have for the oil you say there is no oil sep, what do you have?
    Jun 2002
    628
    AB (Alkylbenzene) Oil is also Miscible with R422D and mixes with the existing mineral oils pre retrofit.
    Jul 2002
    Derby
    22
    It is Poe
    And it is an r22 retrofit
    Fault was the old not achieving temperature
    Has it ever worked properly ? Maybe not since being converted , but I didn't do the conversion
    There is no oil sep at all , close coupled system relying on velocity for return
    I think you may have something with the oil , I don't know how many oil changes etc were done
    I think I will test for mineral oil , but with r422d supposed to work with mineral oil and with a percentage of Poe added im confused why
    Feb 2012
    Bolivia
    270
    14
    -32°C suction + 11° superheat = return gas at -21 not +8 like in your original post.
    When you measure low temperatures in high ambient you should insulate your probe and up and low river so that your sensor and tube take the gas temperature.
    -21°C gas would explain the ice without liquid refrigerant.
    Feb 2012
    Bolivia
    270
    14
    Oh and you should pay attention at defrosts if the oil level goes up in the compressor, your evaporator could be logging too much oil.
    May 2006
    India
    399
    Loose fins of evaporator ???????? Not enough heat transfer .
    Apr 2001
    79
    5,071
    35
    Evap air in temp
    Evap air out temp
    Low side pressure/saturated suction temp
    Suction line temp at TXV bulb
    Cond air in temp
    Cond air out temp
    High side pressure/saturated condensing temp
    Liquid line temp at sight glass
    Jul 2002
    Derby
    22
    Sorry for the late reply, not been on lately
    Appreciate all the replies and help
    Evap air on -10
    Evap air off -13
    Low side pressure 15 psig
    Suction line temp at bulb -10
    Apr 2001
    79
    5,071
    35
    The air flow is okay and the superheat is high. That's about all we can tell without a full set of readings.