    Question Is this tube OK for R410A?



    Hi,

    I'm planning to get some 1/4" and 3/8" tube for a R410A split from here:

    http://www.bes.ltd.uk/products/084a.asp

    Part nos #13998 and #14575 (15 m coils)

    Is this OK for R410A? It states it's made to BS 2871 : Part 2.

    Just that it seems a little thin at 22SWG for the 1/4" and 21SWG for the 3/8".

    Also what would be a sensible bend radius? I was planning to bend it around some appropriate diameter pipe as it's soft copper and so less likely to kink I'd expect.

    Thanks in advance,
    Pete.
    Last edited by smileypete; 01-08-2005 at 04:12 PM.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Is this tube OK for R410A?

    Hi Pete

    I went into NRS (Climate Centre) recently and asked if their soft coiled copper was suitable for the higher pressures of R410a. The manager didn't know what I was talking about.

    We've still been buying the copper though with no ill effects. Maybe the systems haven't been working up to maximum pressures yet but we haven't had any failures so far.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Is this tube OK for R410A?

    I wonder Frank - does the 410 kit expand at the condensing unit or is the high pressure pushed down to the evaporator ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Is this tube OK for R410A?

    Quote Originally Posted by Brian_UK
    I wonder Frank - does the 410 kit expand at the condensing unit or is the high pressure pushed down to the evaporator ?
    On the splits it is at the cond unit but on VRV it is at the indoor unit.

    No bulges in the pipes so far

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Is this tube OK for R410A?

    Guys,
    Acopper tube can hold more then 2000psi before it will burst.

    R22 at 43 out temp in a Chinese split, have the same head pressure that an R 410 split in the UK.
    No problems with the tubes.

    Chemi

  6. #6
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Is this tube OK for R410A?

    I got a sheet from HRP which gives the safe working pressures of their copper tube and also shows which they recommend for use with R410A.

    I have scanned it and would attach it but it exceeds the 100kb limit. I have got it lower but it is then unreadable.

    I have attached it anyway. You can always get the original from HRP

    It isn't safe to say that all pipe will take 2000psi as it depends on the thickness at its thinnest point. A tube that has been bent will be thinner on the outer radius. If the material is also border line on thickness in the first place and is low quality then on a hot day with an overcharged system you could exceed the burst pressure at the weak point.
    Attached Files Attached Files

  7. #7
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Is this tube OK for R410A?

    Quote Originally Posted by BritCit_Juve
    I got a sheet from HRP which gives the safe working pressures of their copper tube and also shows which they recommend for use with R410A.

    .



    Is this the one?

    http://www.hrponline.co.uk/documents...dInfo18xls.pdf

    It?s a few years old, (2000) but mainly still relevant. (BS 4434 is now withdrawn).

    Try contacting the pipe manufacturers. One of the biggest worldwide is Outokumpu.

    http://www.hrponline.co.uk/documents...dInfo18xls.pdf

    They have offices in the UK and should be able to help with queries.

    Generally speaking, refrigeration copper tube off the shelf is suitable for the pressure criteria outlined in EN 378, part 2, up to about 1 1/8 OD, but it?s best to talk to the manufacturers to be certain.

    You need to know if you are within the scope of the PED.


    Good luck
    ________
    Ford Mustang Mach 1
    Last edited by Argus; 07-02-2011 at 08:23 AM.

  8. #8
    Join Date
    Jul 2005
    Location
    UK
    Posts
    60
    Rep Power
    19

    Re: Is this tube OK for R410A?

    Searching through Old Sodd’s Big Book of Practical Jottings, I came across this formula for working out the pipe wall thickness that was circulating some years ago.

    I can’t remember where I stumbled across it, but it seems to do the trick.

    t = [p x d] / [p + (20 x f)]

    t Minimum wall thickness (mm)
    p Allowable Pressure (ps) (barg)
    d OD of the tube
    f Design stress

    The design stress relates to the material and is expressed as a number (N/mm2). The one used for anealed copper tube by convention, as I recall, is 41N/mm2. But it’s worth checking this. Usually the pipe manufacturer should tell you.

    If you’re using a Zeotrope, I suggest that you select the Dew point pressure.

    Bending the tube will affect the stress value on the radius. It’s best to use fittings. I think that's been alluded to before.


    .
    .
    Sodd's the name...... Law's the game.
    Established 1791 - still going strong.

  9. #9
    Join Date
    May 2004
    Location
    London, UK
    Posts
    19
    Rep Power
    0

    Thumbs up Re: Is this tube OK for R410A?

    Hi,

    Thanks for all the replies, looks like it will be fine.

    I'll keep any bends to 6" radius, that would give a maximum thinning by 7% on the outside of the 3/8" tube, though I'd expect the inside of the bend to get a bit thicker too.

    After all the stuff is supplied in coils, so bending it can't be too bad

    The HRP chart for 3/4" 18/19 SWG shows a 20% decrease in safe working pressure for a 20% decrease in thickness from 19 SWG to 18.

    So I'd expect bending 3/8" with a 6" radius should give up to 7% decrease in safe working pressure which should be fine.

    cheers,
    Pete.
    Last edited by smileypete; 03-08-2005 at 05:52 PM.

  10. #10
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Is this tube OK for R410A?

    Hi Argus

    The sheet I tried to scan is dated March 2005 so I assume it has been updated.
    Generally though the info will be the same as you have already got.

    Brit

  11. #11
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Is this tube OK for R410A?

    Quote Originally Posted by BritCit_Juve
    Hi Argus

    The sheet I tried to scan is dated March 2005 so I assume it has been updated.
    Generally though the info will be the same as you have already got.

    Brit



    Thanks, Brit

    I found my link on HRP?s web site yesterday. It?s listed as issue 18, dated 2000.
    There does not appear to be a newer one that I can see, though I would appreciate a copy if possible.

    It?s as well to have the most up-to-date, as the PED has come in since then and the old standard is no longer in use. The requirements are basically the same, but none the less it is out of date. (Why don?t companies keep information on their web sites current?)

    Have you got a link for the new one?

    One interesting point is the arbitrary choice of the two ambient conditions as a basis for the minimum allowable pressure value.
    HRP appear to base theirs on the lower ambient, 32 deg, while a previous poster in the forum quotes a Daikin dealer as recommending using a pressure corresponding to the higher condition of 43 deg. There?s a difference of over 8 bar on R 410A.


    Argus
    ________
    vaporizer manufacturer
    Last edited by Argus; 07-02-2011 at 08:23 AM.

  12. #12
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Is this tube OK for R410A?

    Hi Argus

    The new one isn't online that I can see.
    If you let me have your email address I will send it. Its 364kb so I can't post it here.
    Alternatively contact HRP and request a copy of their Counterparts issue 142. Its dated March 2005

    BritCit_Juve

  13. #13
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Is this tube OK for R410A?

    Ref the ambient choices. HRP don't sell internationally and other than London (all that hot air from westminster) the UK struggles to get anywhere neer 32°C. I suppose therefore they believe the lower limit is safe. Daikin on the other hand sells to the whole world so they need to cover the higher extremes of temperature. To publish the data correctly for every country would be expensive in both time and resources and with copper tube suppliers to do the job Daikin only need to cover their butts for the 99th percentile condition.

    BritCit_Juve

Similar Threads

  1. oxidation scale in copper tube and fittings
    By DeB in forum Fundamentals
    Replies: 8
    Last Post: 23-06-2006, 09:45 PM
  2. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  3. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM
  4. Tube staggered/squared
    By bersaga in forum Fundamentals
    Replies: 2
    Last Post: 05-01-2003, 11:56 PM
  5. coaxial (tube in tube) heat exc.
    By aliugur in forum Fundamentals
    Replies: 0
    Last Post: 04-06-2002, 08:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •