27-04-2012, 05:31 AM #1
Carrel i33
I need help with a new carrel i33 platform controller I installed with new probes.after verifying all wires connections are correct and the control is programmed correctly, the compressor would not run. After checking wires and settings the compressor would run but with no compressor icon display. And the temp read 10-15 degrees lower the the actuall cabinet temperture on the control. I am thinking I somehow locked the control settings or the control is bad out of the box? And is their a override or correction that can be done ? Any help would be appreciated
-
27-04-2012, 09:17 AM #2
Re: Carrel i33
Read this slowly and find where you went the wrong way.
http://www.scribd.com/doc/53319285/carel-ir33-manual
-
27-04-2012, 07:43 PM #3
Re: Carrel i33
carel controllers accept a few types of probes- ntc ,ptc, you prob need to adjust the probe type-see chemi's link
-
28-04-2012, 10:31 PM #4
Re: Carrel i33
search the site carel.com
-
02-05-2012, 12:02 PM #5
Re: Carrel i33
You can contact Carel UK directly on 020 8391 3540 and ask to speak to their technical help desk.
The IR33 platform uses NTC probes as standard however some models of IR33 can accept other probe types, the range of controllers on the IR33 platform is quite extensive.