    Carrel i33



    I need help with a new carrel i33 platform controller I installed with new probes.after verifying all wires connections are correct and the control is programmed correctly, the compressor would not run. After checking wires and settings the compressor would run but with no compressor icon display. And the temp read 10-15 degrees lower the the actuall cabinet temperture on the control. I am thinking I somehow locked the control settings or the control is bad out of the box? And is their a override or correction that can be done ? Any help would be appreciated



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Carrel i33

    Read this slowly and find where you went the wrong way.
    http://www.scribd.com/doc/53319285/carel-ir33-manual

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Carrel i33

    carel controllers accept a few types of probes- ntc ,ptc, you prob need to adjust the probe type-see chemi's link

  4. #4
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    77
    Rep Power
    13

    Re: Carrel i33

    search the site carel.com

  5. #5
    Join Date
    Nov 2008
    Location
    England
    Posts
    5
    Rep Power
    0

    Re: Carrel i33

    You can contact Carel UK directly on 020 8391 3540 and ask to speak to their technical help desk.

    The IR33 platform uses NTC probes as standard however some models of IR33 can accept other probe types, the range of controllers on the IR33 platform is quite extensive.