    Prem-i-air PMSF12 - No cold air



    Hi,

    Hoping you can help.

    Firstly I am in no way a refrigeration engineer so my assertion maybe completly wrong so please be gentle!

    I have had a Prem-i-air PMSF12 - DIY split unit with quick connect couplings for about 4 years.

    Up until about 1 week ago it was working perfectly, however it has now stopped blowing cold air.

    Things I have checked:

    1) Internal filter is cleaned about every month and is clean

    2) external unit about the same

    3) external unit and internal unit are powered and both fans are blowing.


    - My guess is that it needs a recharge of R410A - 1100g?

    Two questions

    1) Does a recharge sound logical?

    2) I have had a quote for about £250 including 2 hours work vacumn,recharge and pressure test is that ok?

    3) Will the fact that it has quick connects effect the engineers ability to recharge?


    Thanks for your help.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Prem-i-air PMSF12 - No cold air

    qwik couplers are the work of the devil- the o rings deteriorate with heat, you say both fans are running,can you hear the compressor run?-most small cheap units dont have a low pressure switch- normally just the compressor overheats after a while- is there any signs of oil anywhere-this would indicate a leak.

  3. #3
    Join Date
    Apr 2012
    Location
    London
    Posts
    3
    Rep Power
    0

    Re: Prem-i-air PMSF12 - No cold air

    Hi,

    Thanks for replying so quickly - yes I can hear the compressor switching on - but I cant hear the fizzing and the poping that I used to.

    Feeling the metal "fins" (evaporator?) on the internal unit its not cold at all.

    However I have just looked outside and can see condensation on the quick connection couplings.

    No oil can be seen on the floor under or surrounding the external unit

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Prem-i-air PMSF12 - No cold air

    first ensure they weigh the gas they remove to compare this to the factory charge-usually around 1.1kg
    then if they weigh out the correct charge then possibly compressor failure-not pumping or partial blockage
    if no gas or lost gas from the system then pressure test to find and fix the leak-vac system and weigh in new gas.
    found a technical support details for you
    Product Support
    Email :
    helpdesk@prem-i-air.co.uk
    Telephone :
    01744 745030
    Fax :
    01744 745001

  5. #5
    Join Date
    Apr 2012
    Location
    London
    Posts
    3
    Rep Power
    0

    Re: Prem-i-air PMSF12 - No cold air

    Thanks again for your help.