Looking at pics, there is heavy ice build up on distributor tails for +2'C room. They should be reasonably clear of ice if feeding correctly and distributor orifice and tail length and diameter are sized correctly. Suggest that the selection of total pressure drop across TXV distrib orifice and tails is too low and TXV will be hunting. The EPR is masking the real problem.