Thread: Pressure testing
-
21-07-2005, 08:47 PM #1
Pressure testing
What is recommended pressure test for Daikin VRVII and can the s/o valves withstand the pressure?
Jase
-
21-07-2005, 08:55 PM #2
Re: Pressure testing
Spaceair recommend 40barg on their traning course.
They also recommend that you make sure the service valves are shut tight before you test.
-
26-07-2005, 05:16 PM #3
Re: Pressure testing
Pressure testing criteria is covered in an European Standard, EN 378, part 2.
This standard is harmonised to the PED. The requirements are not too complex.
Not certain if the VRF system you mention is within the scope of the PED, it may not be, but the criteria are good practice, and it is a recognised methodology that you can sign off on your commissioning sheets..
Sodd's the name...... Law's the game.
Established 1791 - still going strong.
-
26-07-2005, 06:55 PM #4
Re: Pressure testing
Originally Posted by Sir Josiah Sodd
-
27-07-2005, 09:16 AM #5
Re: Pressure testing
Originally Posted by Krups
I'll do my best, which parts, Mr Krupps?.
Sodd's the name...... Law's the game.
Established 1791 - still going strong.
-
27-07-2005, 12:50 PM #6
Re: Pressure testing
Mmmm...
Yes exactly,but I am quite pleased with Franks reply.At the end of the day all I am concerned about is whether the system in question is capable of withstanding a reasonable high pressure test over a given time scale, say 48 hours plus e.g
Also as Frank had mentioned the the pressure test which is recommended has came from a Daikin distributor and so when attending these training courses they never mention anything about european standard codes of practice.All they tell you is the recommended pressure test for there equipment
Regards
Jase
-
27-07-2005, 03:35 PM #7
Re: Pressure testing
.
40 bar?
That's almost 600 psi in old money!
Anyone from Daikin Europe lurking in the background, care to comment?
The standard I mentioned provides 2 operating conditions, 32 & 43 degrees. you can work the rest out for yourself. If the gas is Zeotropic, you select the pressure corresponding to the Dew point temperature
..
Sodd's the name...... Law's the game.
Established 1791 - still going strong.
Similar Threads
-
Pressure testing for leaks on split a/c systems
By mrchatts in forum Air ConditioningReplies: 46Last Post: 08-04-2010, 10:02 AM -
Pressure testing
By Chopper in forum IndustrialReplies: 8Last Post: 24-10-2005, 06:40 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Pressure Testing
By Derek in forum Technical DiscussionsReplies: 6Last Post: 09-07-2001, 07:11 PM