    Carlyle 06NA reversing



    Hi

    I have a problem with a Carrier 30HXC Chiller . Each of the two circuits has two Carlyle 06NA compressors. On switching off , one of the compressors reverses rotation due to gas back flow.
    ( The whining noise of the screws reversing). My first assumption was that the discharge check valve was stuck or damaged. On inspection and testing the discharge valve sealed tight and showed no damage. Tests where carried out with the check valve housing removed from the compressor.
    My only idea is that there is not enough back flow of gas to push the plunger on the seating when the compressor switches off.
    Any help would be greatly appreciated as this compressor works fine except for this problem.

    Thanks​



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Carlyle 06NA reversing

    Screw compressors are designed to run backwards when they stop... Reverse Thrust

    its the other three that dont reverse thrust when stopped that need looking at

    R's chillerman
    Last edited by chillerman2006; 18-03-2012 at 08:12 PM.
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Apr 2008
    Location
    Malta
    Age
    67
    Posts
    9
    Rep Power
    0

    Re: Carlyle 06NA reversing

    Thanks for the reply.
    We have a chiller farm with 14 30HXC chillers installed and not one compressor reverses in this way when stopped.I would expect a small ammount of reverse until the check valve closes but this compressor goes on for about 10 seconds and that is way too long.