    condenser fans won't stop running k control mr slim ?



    hi guys, wonder if you could help out? got an old mr slim cassette found a p8 fault on the controller. Checked outdoor unit found the glass fuse on the PCB blown, replaced and condenser fans came on strait away. unit started and is running fine.
    but when i turn it off from the controls the condenser fans constantly run!
    could it be a problem with the pipe thermistor ? to my knowledge doesn't this control the fan speed/ cycle?



  2. #2
    Join Date
    Feb 2012
    Location
    Australia
    Age
    44
    Posts
    3
    Rep Power
    0

    Re: condenser fans won't stop running k control mr slim ?

    P8 could mean a saftey device worked like HP. Or could be damage coil thermistor.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47

    Re: condenser fans won't stop running k control mr slim ?

    Hi roznic.

    Check out the following.

    Attachment 8714

    Abnormality of pipe temperature.
    Not my area, but I would suspect maybe a high discharge temp which would drive the condenser fans?

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: condenser fans won't stop running k control mr slim ?

    or relay on outdoor pcb welded- unplug the 2 fan connectors and test continuity from the fuse to the live out to the fan- isolate it first though

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47

    Re: condenser fans won't stop running k control mr slim ?

    Quote Originally Posted by install monkey View Post
    or relay on outdoor pcb welded- unplug the 2 fan connectors and test continuity from the fuse to the live out to the fan- isolate it first though
    Thanks for the extra advise its appreciated,well at least from me!
    Grizzly.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: condenser fans won't stop running k control mr slim ?

    https://rapidshare.com/files/2902456...r_slim_r22.pdf;
    2 dipswitches on the outdoor will give u the coil temp- p8 is outdoor abnormality- ceck for flashing led on outdoor pcb or it will alarm p8 if indoor room temp doesnt change in 15 mins- ie dirty filter - blocked vents- etc
    Last edited by install monkey; 14-03-2012 at 10:23 PM.

  7. #7
    roznic's Avatar
    roznic Guest

    Re: condenser fans won't stop running k control mr slim ?

    thanks monkey.

    I'll check that next time im round there.
    i unplugged the pipe thermistor to see if the fans cycled off but didn't.
    I'll try the continuity.