Results 1 to 14 of 14
08-02-2012, 01:27 PM #1
CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle
Hi guys
i am working on a chinese automatic ice machine called : CRYSTAL ICE 603A,when plug in the power, the unit runs , but suction pressure drops , then unit shuts down. unplug the power ,few minutes later plug in the same prob. the water side is ok.
i think the unit stuck in def sycle or some sensor is faulty,causing the valve to close, as it is fully automatic, i initiate the automatic reset to no avail, i can not find any source to download fault code or refer to service manual.
i think the manufacturer or suppliers are in hong kong called ypt international ltd,
any help?Last edited by sork; 08-02-2012 at 02:01 PM.
08-02-2012, 07:34 PM #2
Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle
Could be a contol problem or lack of refrigerant, google ypt international hongkong.
08-02-2012, 08:07 PM #3
the unit stuck at the end of harvest, i checked ref 404a, the unit stops valve kicks up, i need to download the basics for it, i check the exp valve everything is ok. it is fully automatic, do not know how and where the suppliers are in uk.
08-02-2012, 08:10 PM #4
crystal ice automatic ice machines CTM603A MODEL, originally chinese , most parts for are are european.
09-02-2012, 06:55 AM #5
09-02-2012, 09:41 AM #6
no ice no refrigeration takes place, unit starts , immidiatly suction pressure drops to zero, mag vale kick off , comp stops, thst is all. to restart, unplug and plug the power, the above happens.
09-02-2012, 07:42 PM #7
mikeref you might be right, i took the pc to check, i was thinking it might be the sensors.
11-02-2012, 05:44 PM #8
i have tried the above no luck.
13-02-2012, 02:49 AM #9
So it locks out on Low pressure. Remove and weigh gas charge. Drier might have fragmented and blocked cap tube(s). I'm not familiar with this brand of ice-maker.
13-02-2012, 09:07 AM #10
i have change the dryer, recharged, check exp valve, the unit still cutting out on LP switch.
15-02-2012, 04:56 PM #11
it is a crystal ice automatic ice machine.CTM603A, metering device is tev
when i turn unit on, the waterpump starts and sprays the water to evaporator, then,waterpump stops, compressor starts, suction pressure drops, compressor shuts down.
anyone help???
01-03-2012, 07:49 PM #12
thanks guys
the unit is mv 306 scotsman , the fault was the the mag switch and the blockage in thge filter dryer. machine was identified by the people in hong kong.
01-03-2012, 10:45 PM #13
Hi Sork.
problem solved thanks for coming back to us.
So is it a Scotsman made in china, rebranded or name badge engineering.
02-03-2012, 08:03 PM #14
yes absolutely right. the blockage on the orifice of the tev caused confusion plus other minor adjustments.