    CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle



    Hi guys
    i am working on a chinese automatic ice machine called : CRYSTAL ICE 603A,when plug in the power, the unit runs , but suction pressure drops , then unit shuts down. unplug the power ,few minutes later plug in the same prob. the water side is ok.
    i think the unit stuck in def sycle or some sensor is faulty,causing the valve to close, as it is fully automatic, i initiate the automatic reset to no avail, i can not find any source to download fault code or refer to service manual.
    i think the manufacturer or suppliers are in hong kong called ypt international ltd,
    any help?
    Last edited by sork; 08-02-2012 at 02:01 PM.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    Could be a contol problem or lack of refrigerant, google ypt international hongkong.

  3. #3
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    the unit stuck at the end of harvest, i checked ref 404a, the unit stops valve kicks up, i need to download the basics for it, i check the exp valve everything is ok. it is fully automatic, do not know how and where the suppliers are in uk.

  4. #4
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    crystal ice automatic ice machines CTM603A MODEL, originally chinese , most parts for are are european.

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    Quote Originally Posted by sork View Post
    the unit stuck at the end of harvest, i checked ref 404a, the unit stops valve kicks up, i need to download the basics for it, i check the exp valve everything is ok. it is fully automatic, do not know how and where the suppliers are in uk.
    Ice stuck on evaporator or stuck in door so circuit not closed for new cycle? Alignment and possible foreign matter on harvest door making P.C. stop at that point.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    no ice no refrigeration takes place, unit starts , immidiatly suction pressure drops to zero, mag vale kick off , comp stops, thst is all. to restart, unplug and plug the power, the above happens.

  7. #7
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    mikeref you might be right, i took the pc to check, i was thinking it might be the sensors.

  8. #8
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    i have tried the above no luck.

  9. #9
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    So it locks out on Low pressure. Remove and weigh gas charge. Drier might have fragmented and blocked cap tube(s). I'm not familiar with this brand of ice-maker.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  10. #10
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    i have change the dryer, recharged, check exp valve, the unit still cutting out on LP switch.

  11. #11
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    it is a crystal ice automatic ice machine.CTM603A, metering device is tev
    when i turn unit on, the waterpump starts and sprays the water to evaporator, then,waterpump stops, compressor starts, suction pressure drops, compressor shuts down.
    anyone help???

  12. #12
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    thanks guys
    the unit is mv 306 scotsman , the fault was the the mag switch and the blockage in thge filter dryer. machine was identified by the people in hong kong.

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    Hi Sork.
    problem solved thanks for coming back to us.
    So is it a Scotsman made in china, rebranded or name badge engineering.

  14. #14
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle

    yes absolutely right. the blockage on the orifice of the tev caused confusion plus other minor adjustments.