    Daikin Indoor Fan



    Had a call today on a Daikin AC System (indoor - FCQH125C7VEB), controller showing A6 Fault code which is indoor fan motor, can anybody tell me what the DC voltage is supposed to be for these fans?? I got 335V DC off the board to the fan and just want to confirm thats the correct voltage before i go ahead and order a new fan motor, its been about 2 years since i worked on daikin so im pretty rusty, thanks in advance!!



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin Indoor Fan

    For most (well all the ones I've come accross)
    Pin 1 Red wire - DC 330V
    Pin 2 Empty
    Pin 3 Empty
    Pin 4 Negative
    Pin 5 15V DC to power internal PCB
    Pin 6 Command voltage indicating what speed to run fan
    Pin 7 Output pulse of actual fan speed

    Pins 5,6 and 7 are sometimes swapped about depending on make.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    Oct 2008
    Location
    UK
    Age
    39
    Posts
    174
    Rep Power
    16

    Re: Daikin Indoor Fan

    Thanks Andy, that pretty much confirms it as i got the 330v DC between red and blue so the fan has power but it wasnt doing anything. Cheers!!

  4. #4
    Join Date
    Oct 2008
    Location
    UK
    Age
    39
    Posts
    174
    Rep Power
    16

    Re: Daikin Indoor Fan

    The indoor unit is fed off a VRV and i havent done much work at all on VRV systems mainly splits, when i isolate the indoor unit to replace the fan im guessing the system will throw up a transmission error? if so will i need to reset the outdoor unit to clear the fault or will it pick up the indoor unit when i turn it on and reset itself? If i do need to reset the system what is the method of reseting daikin VRV systems is it a simple case of switching the outdoor unit off for 30secs then back on???
    Last edited by Northdude; 04-02-2012 at 06:03 PM.

  5. #5
    Join Date
    Oct 2008
    Location
    Serbia
    Posts
    16
    Rep Power
    0

    Re: Daikin Indoor Fan

    1. Disconnected or faulty wiring between fan motor and PC board : Fix the wiring and turn on again.
    I have problem on one FXFQ125P9VEB produced in Novemmber 2011

    2. Replace the indoor unit PC board.
    I have problem on one FXFQ100P9VEB produced in Novemmber 2011

    broken PCB
    Parts No. 5002452 PCB ASSY ( Drawing No. 2P222924-5 ) on FXFQ100P9VEB
    After changing of PCB and 301440P WIRE HARNESS ASSY ( 4PW31004-1 ) unit was repaired.