    Biggest electric motor on refrigeration compressor/s
    Whats the biggest motor you have seen or worked on in refrigeration?
    I know there is some big stuff out there, so interested to hear.
    Apr 2008
    Southampton, England
    49
    1,023
    Re: Biggest electric motor on refrigeration compressor/s
    Biggest for me was a Dunham Bush water chiller. Part wound compressors - don't know what size but most of the 100A fuses were blown because they remaining 2 compressors (out of 4) were down to earth.
    Messed about with an old air handler at Centre Parks, Longleat. Looked like it was made about the same time as Noah's Ark. They were star/delta motors. Clamped a cable on startup and it was over the scale of the meter (100A) then settled down to 50. Stood inside the handler when it was running - probably explains why most of my hair is missing.
    Cheers,
    Andy.
    Jul 2005
    61
    68
    4160 volt 1000HP
    Jun 2011
    Australia
    44
    336
    425 kw on Howden 255 long rotor, but I'm sure there are plenty bigger.
    3,363
    There is a process ammonia plant I worked on but not this particular unit.
    Its a double shaft high voltage motor, on one end is a Mycom 320L & the other end through a reversing gearboxis another Mycom 320L.
    Its motor is about 2800kw
    3,853
    Biggest i worked on was a 40hp copeland! and that was big enough!
    Croatia
    68
    2,261
    Hi. all
    ... till now ...
    Howden 321 with R1270 (-20*C/+47*C) and Ansaldo motor of 1600 kW at 3570 rpm
    ... next one is about 2300 kW
    Best regards, Josip
    Sep 2009
    Iran
    66
    674
    1
    400 kw in ice block machine with 450 rpm 30 years ago I think it was york or ... ,
    but biggest machine room I installed has a 750 hp wit 5 compressor on it NH3.
    good job I did. 100 ton per day chlorine liquid system last year .
    Nov 2010
    London
    624
    300A on 3000V 3Ph
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
    Nov 2010
    London
    624
    Here's a centrif starting up. These can be run off of 3000V at about 50 to 60 amps.
    The chiller can be heard surging soon after the guide vanes open. The tech goes back to lower the limit on the chiller loading to avoid the surge area. Perhaps until the purge unit has cleared air from the system.
    http://youtu.be/LJlDaFrvKQ0
    Sep 2008
    427
    Just follwed a link on there and found this!!!!
    www.youtube.com/watch?v=-5MH5shs-FU&feature=related
    i`ve done some things in my time but i think I`ll be giving this a miss
    70
    4,700
    47
    Hi Glenn.
    That guy is some kind of idiot!
    What would happen if the drive shaft friction welded itself to the fan blades.
    His engineering practices are as ancient as the kit he is working on.
    Scary stuff.
    But good post all the same.
    Thanks Grizzly
    Dec 2011
    Ireland
    44
    I'm lost for words after watching that video, what an idiot...
    Oct 2006
    1,843
    Grimsby ice house.
    Largest refrigeration plant in its day.
    The motors below left are still there in situ. bottom right are similar motors.
    More than 1000hp and there were started manualy
    3,363
    Work on one plant with a few S75 Stal screws.
    DOL high voltage 800 hp.
    The coupling hubs on compressor have no key, so uses a hydraulically driven taperlock to secure on shaft.
    The hydraulic pump to drive it on goes up to 30 000psi.
    You measure outside of taperlock to a certain growth measurement to determine if taper is driven
    on far enough.
    Personnally would use a keyway, but seems to be the trend on European screw compressors Stal, Grasso,Sabroe.
    Usually **** myself with worry, as know consequences if you get it wrong, especially after full overhaul.
    Feb 2012
    Italia
    1
    I work in a company that manufactures and sells industrial refrigeration systems, my work was in the Department of assitance machines, I have seen very large machines such as Howden WRV 321, 320 lud Mycom, 32 llnb kobelco etc ... these machines were combined with electric motors abb, leroy somer etc from 415 kW, 500 kW and 750 kW at low voltage (400 volts) mind from 1000 kW 1250 kW Medium voltage normally. In my work I ritch serviced more than 1000 machines all over the world like this. Sorry for my English.
    38
    Hi Ranger1.
    A mycom 320 booster auto trani starter, never started with the MCC panel open, the fault rating at start up was horrendous, I think is was 385 Kw low voltage. On first start in rush currents took out site transformer and local area supply transformer, we weren't very popular. Way back commissioned a couple of 3.3kv centrifs, what a performance, the first commissioned with live startup took out the site transformer protection despite the electrical engineers assurances that he had set them up correctly. The down side was that the site was a hospital, you would not beleive the greif that created.
    Oct 2008
    newbury
    1,444
    Largest were several Carrier 19DR centrifs at gatwick airport as part of an on site maintenance team. Approx 1800TR or 6500kw cooling duty each IIRC
    Not for me and I kept away from them as much as possible as I don't like really big stuff..
    Sep 2008
    427
    I`m about to change jobs to a site that has 3x 750kw air compressors, I hope a motor change doesn`t arise as they go 2.5 tons each
    Sep 2008
    427
    I remember seeing those a few years back. I`m not sure but I think at the time were they on R12!
    Oct 2008
    newbury
    1,444
    Quote Originally Posted by glenn1340 View Post
    In the old terminal plant room they were R11...........In the North terminal (which were going in when I was there) I think they were on 134a but not sure..
    Jun 2010
    Yorkshire
    59
    520
    Harland Simon 750 horse dc tandem and a 3.3kv 1.8kw ac, that was in a rubber compounders. On refrigeration 80 kw Carlisle central unit (open compressor), it was charged with etha, nobody told us and we found out the hard way!
    Training may be finished but experience is never complete.