    Increasing system capacity



    I have a situation where the air cooled split system does not handle the load.
    On the hot days the space temp goes up to 27 deg C.
    Due to space limitations its impossible to install another unit.
    It was suggested to install a DX coil in the Return Air duct to drop the RA temp down to say 23C.
    Not sure what the problems are in regard to this and how to control it.
    Any suggestions?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Increasing system capacity

    Install a an evaporative pre-cooler before the outdoor air inlet.

  3. #3
    Join Date
    Feb 2012
    Location
    Australia
    Posts
    4
    Rep Power
    0

    Re: Increasing system capacity

    Quote Originally Posted by mad fridgie View Post
    Install a an evaporative pre-cooler before the outdoor air inlet.
    Nocando humidity too hi on Australian east coast for evap cooler to work.

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Increasing system capacity

    Not an evap cooler, "direct" just prior to condenser inlet. "Spray/mister nozzles"

  5. #5
    Join Date
    Feb 2012
    Location
    Australia
    Posts
    4
    Rep Power
    0

    Re: Increasing system capacity

    Looking for increase of 50% not 5%

  6. #6
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Increasing system capacity

    it sounds like your system is way under capacity. is there any chance you could slip another coil next to the other one in front or behind and plumb that up to another condenser unit? where abouts in Aus are you?