    citi multi defrost issue



    Having a problem with my citi multi. when the temperature gets colder (below 25) the unit defrosts quite frequently (every25-35 minutes) and the defrosts are quite long (7-18 minutes) my issue is any of the 4 indoor units that are calling for heat it runsthe fans on low after shutting off briefly regardless of the coil temperature and I am getting 45 degree air temperature coming from the units which cools the room down about 10 degrees during defrost. Obviously I am getting many complaints from guests, I don't think the system was designed to do this but the local and regional reps have no solutions for me can anyone help?



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    26

    Re: citi multi defrost issue

    Hi Tomp
    First up You can change the defrost start/stop temp on the outdoor board , see attached manual pg44.
    SW3-3 and SW3-4
    You can also change the defrost prohibit time SW2-8
    And the indoor fan can be taken back to ultra low SW1-7 off(indoor board)

    https://rapidshare.com/files/2601380...multi_y_r2.pdf

    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Jan 2012
    Location
    United States
    Age
    62
    Posts
    2
    Rep Power
    0

    Re: citi multi defrost issue

    Thanks for the reply, I assume from your response the fans on the indoor units cannot be stopped from blowing the cold air (ultra low is the best we can do) is that correct?

  4. #4
    Join Date
    Jan 2012
    Location
    ENGLAND
    Age
    49
    Posts
    6
    Rep Power
    0

    Re: citi multi defrost issue

    Quote Originally Posted by tomp View Post
    Thanks for the reply, I assume from your response the fans on the indoor units cannot be stopped from blowing the cold air (ultra low is the best we can do) is that correct?
    This is correct, fans can only be set to off during thermostat off.

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    26

    Re: citi multi defrost issue

    Sorry Tomp been away for a few days , as Zeppers said fan only off during thermo off.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    Join Date
    Dec 2008
    Location
    Los Angeles
    Posts
    32
    Rep Power
    0

    Re: citi multi defrost issue

    It is possible to turn off the IDU fan during heat mode if thermally off. See your Mitsubishi Tech Support agent for details on your particular IDU model. But...

    SW 3-1 OFF, SW1-7 ON, SW1-8 ON = Fan Stop in Heat Mode

    If experiencing low heat or extended defrost, I would double check the application and expected Btu's of the system via Design Tool.

    Another check would be the charge. Use Maintenance Tool for verify pressures and temperatures are within range for the given ambient temperature.