Results 1 to 6 of 6
Thread: Carrier 30XA Oil Filters
-
03-02-2012, 10:43 PM #1
Carrier 30XA Oil Filters
Can anyone suggest why we have had to change 3 oil filters in 2 weeks on both of the compressors of our machine.
We are running at -12C and using Coolflow LV30 as the coolant
-
03-02-2012, 10:53 PM #2
Re: Carrier 30XA Oil Filters
OK, why did you have to change the oil filters, what prompted that action?
We can't see your machine from here and don't know the running conditions or states.
The LV30 is the secondary refrigerant and is not connected with the oil in the primary side.Last edited by Brian_UK; 03-02-2012 at 10:56 PM.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
04-02-2012, 11:32 AM #3
Re: Carrier 30XA Oil Filters
Probably you have a very contaminated (burnout debris etc) frigo lines.
Changed any comps lately?
-
04-02-2012, 08:40 PM #4
Re: Carrier 30XA Oil Filters
Hi taylok.
My info dated 2008 says that the range for the 30XA is -10c to +55c am I missing something?
Grizzly
-
04-02-2012, 10:11 PM #5
Re: Carrier 30XA Oil Filters
There is a factory option for -12c using ethylene glycol, -10c to +55c is ambient i think
-
04-02-2012, 10:28 PM #6
Re: Carrier 30XA Oil Filters
Which oil filters are you changing internal or external, what alarms are you getting ?