    PUHYP400MFB Indoor Units Stay in Cooling



    Hello,
    I'm working on a Mitubishi PUHYP400MF-B which is connected to a Procon Y-ACO. From what I can gather the Y-ACO has a room sensor and dictates whether the outdoor unit runs in heating or cooling. My problem is that even when I raise the temperature on the Y-ACO and the green light goes off (indicating heating) the indoor units remote will not go into heating, they stay in the cooling mode even if the remote setpoint is raised. I would appreciate ny help with the above.



  2. #2
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: PUHYP400MFB Indoor Units Stay in Cooling

    Indoor unit SW 3-1 may set to ON (Cooling only instead of Heatpump). (Unlikely but check)

    Check on Outdoor's Auto change over CN3N (3wire adaptor cable)

    1 and 2 short/closed >> heating only
    1 and 3 short/closed >> cooling only

    Most likely Procon interlock with this.

    Hope this will help.

  3. #3
    Join Date
    Oct 2011
    Location
    Bromsgrove, Worcs
    Posts
    33
    Rep Power
    0

    Re: PUHYP400MFB Indoor Units Stay in Cooling

    Thanks JoeAT50A,
    i'm due back next week so i shall have a look then

  4. #4
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    26

    Re: PUHYP400MFB Indoor Units Stay in Cooling

    Check the dead band setting on the YACO.
    Mode shift is set point +/- dead band depending on original mode to avoid space temperature swings.
    Is the controller in Automatic mode??
    Cheers
    Stu