Results 1 to 3 of 3
  1. #1
    Join Date
    Dec 2011
    Location
    republic of yemen
    Age
    48
    Posts
    3
    Rep Power
    0

    heat load calculation formula...anyone could share?



    dear friends,

    I would like to know the heat load calculation formula for the remaining heat load factors i am considering in a Machinery room with 3 packing machines rating 4.5kw each, the dimensions of room are L= 5m ; W=10m ; H=5m? I calculated already the other factors namely occupants heat load, lighting heat load. What to be consider also is the 2 doors which are 2m x 2m size. TY for whatever useful help you can relay.

    regards,
    fernan



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: heat load calculation formula...anyone could share?

    Hi Fernan

    Not complete data but maybe some help, see page 30

    http://www.bre.co.uk/filelibrary/pdf...Edition%29.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: heat load calculation formula...anyone could share?

    All you need is the building fabric transmission load. To calculate this you need to know the indoor temperature, the outdoor temperature and fabric U values of the walls, floor and roof

    You also need to know the ventilation infiltration rate