Results 1 to 3 of 3
-
01-02-2012, 02:48 PM #1
heat load calculation formula...anyone could share?
dear friends,
I would like to know the heat load calculation formula for the remaining heat load factors i am considering in a Machinery room with 3 packing machines rating 4.5kw each, the dimensions of room are L= 5m ; W=10m ; H=5m? I calculated already the other factors namely occupants heat load, lighting heat load. What to be consider also is the 2 doors which are 2m x 2m size. TY for whatever useful help you can relay.
regards,
fernan
-
01-02-2012, 08:53 PM #2
Re: heat load calculation formula...anyone could share?
Hi Fernan
Not complete data but maybe some help, see page 30
http://www.bre.co.uk/filelibrary/pdf...Edition%29.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
02-02-2012, 08:31 PM #3
Re: heat load calculation formula...anyone could share?
All you need is the building fabric transmission load. To calculate this you need to know the indoor temperature, the outdoor temperature and fabric U values of the walls, floor and roof
You also need to know the ventilation infiltration rate