    Ice cream display case set at -13.5Stock at one end very hard, Other end very soft. All fans running in The same direction. 2 defrosts per day for 15 minsTo defrost fallen icecream. Why is the stock varying in temp so much?
    manchester
    5,639
    Re: Ice cream display case problems.
    faulty stat,compressor overheating or short of gas
    Dec 2010
    devon
    837
    is it a straight case or a multideck version
    lucaskeating Guest
    It is a straight case, full sight glass at all times, if it hadA faulty stat wouldn't we still see a uniform temp in the case?Has worked previously.
    Jul 2010
    manchester
    212
    Is half of the evap coil iced up ?
    when you say straight case? what type of freezer is it?
    hot gas defrost? elec defrost?
    is the case defrosting correctly?
    defrost time seems short for 2 defrosts per day, what is the defrost term temp set to?
    your only as good as your last job
    Apr 2006
    55
    1,908
    30
    Air flow maybe
    Can the air fully circulate the load, nothing stacked on the floor or against the wall
    manchester
    5,639
    are the defrost heaters staying on? contactor/relay welded!!
    Dec 2010
    devon
    837
    first step is lower the setpoint minus 13.5 aint enough for icecream
    Sep 2011
    84
    14
    Are the brands of ICe Cream different from end to end. I have always seen that higher end ice cream is harder to freeze
    38
    Holding temp for ice cream is -20'C, storage temps between -29 and -26'C
    manchester
    5,639
    around -13 its easier to scoop up as opposed to the solid block in ur own freezer
    Dec 2010
    devon
    837
    cant agree there install minus 13 thats to soft for all our customers mate the problem set at minus 13 it aint cutting in untill minus 11 and it aint running long enough to ice the evap all the way thats why it may have such a temp diff in chamber set to minus 18 and let it settle most of the isa and framecs only df twice a day and the reason for high end ice cream requires more freezing is it useually contains more sugar or alcohol
    Oct 2011
    Heat source or direct sunlight at one end?
    gasrepser's Avatar
    gasrepser Guest
    what is your superheat