    Trouble Shooting Cascade system W/Cap tube SO LOW U85-18



    Hi, Interesting problem. The So-Low is a two-stage Cascade system w/Cap tubes. The system Has two 1HP compressors. The problem I'm experiencing is as follows. Unit Thermostat is set to Minus-40 Deg C. Unit starts normally, and runs down to setpoint. After shutting down at setpoint there is, of course, a deadband idle time. After idle period, unit tries to resume setpoint . Immediately upon restart, unit blows 20-Amp wall breaker. I cannot understand why start from scratch operates properly, but resumption of operation causes this symptom. I guess my question is: What can cause this, and how can I isolate problem. Thanks to anyone with experience in this matter.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Trouble Shooting Cascade system W/Cap tube SO LOW U85-18

    Is the low side compressor trying to start without the high side already running?

    You say 'idle period', is this a set time period or "just an expression"?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Trouble Shooting Cascade system W/Cap tube SO LOW U85-18

    how long is the delay before restarting-should be at least 3 mins

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Trouble Shooting Cascade system W/Cap tube SO LOW U85-18

    Hi Aero
    Capp systems use low start torque compressors and require time for the pressures to equalise. You could use a fluke current meter with logging of max current to confirm, could also be starting gear on comp giving you trouuble.

  5. #5
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Trouble Shooting Cascade system W/Cap tube SO LOW U85-18

    is it set for -40 in the cabnet or is the heat exchanger set for -40 therefore bringing on second stage compressor to cool the cabnet?