    Question fujitsu inverter doesn't start when the outdoor temp is below zero



    hello my friends!
    Does anyone know why a fujitsu inverter ,24000 btu -R 410 ,doesn't start operating when the ambient temperature is below 0 Kelsium?
    During the day when the temperature rises it operates normaly as usual in heating mode.
    Thanks a lot!



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: fujitsu inverter doesn't start when the outdoor temp is below zero

    Faulty outdoor sensor?

  3. #3
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: fujitsu inverter doesn't start when the outdoor temp is below zero

    maybe, but it generates me many questions why this is always happening at the dawn when temperature is below zero.I suppose that the control cuts the system as a protection from icy conditions.
    However, this is not correct since the system is inverter (designed to operate at low temperatures) and next to fujitsu is installed a daikin inverter split(in another room) that operates without any problem at all.

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: fujitsu inverter doesn't start when the outdoor temp is below zero

    The moral is Daikin is better than Fujitsu

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: fujitsu inverter doesn't start when the outdoor temp is below zero

    any flashing lights on the indoor unit? try holding the outdoor sensor when its not running to see if it starts