    what is common application of A quench valve or temperature responsive?

    thanks



  2. #2
    maniam chinniah's Avatar
    maniam chinniah Guest

    Re: A quench valve ?

    quench valve is to just cool down the compressor coil

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: A quench valve ?

    Quote from Carrier documentation...

    +
    During periods of low load, the suction modulating valve decreases flow of refrigerant to the compressor. This
    action balances the compressor capacity with the load and prevents operation with low coil temperatures. In
    this mode of operation, the quench valve will open as required to provide sufficient liquid refrigerant flow into
    the suction line for cooling of the compressor motor. The quench valve senses the temperature of refrigerant
    entering the compressor and provides additional coolant to the compressor motor.
    +
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: A quench valve ?

    never heard of the term !!quench valve!! but from reading what brain has posted isnt that basically what a liquid injection valve in some applications does in order to decrease the superheat at the compressor.
    your only as good as your last job

  5. #5
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    14

    Re: A quench valve ?

    Hi,

    I am also not aware about the term "Quench Valve " .But i also feel that its performing the same function as liquid line is injected into compressor motor even it has expansion valves which regulates the flow of liquid refrigerant. If there is any difference , then please let me know.

    Thanks for your cooperation.

    Cheers

    SUMIT

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: A quench valve ?

    Quote Originally Posted by cold.man View Post
    never heard of the term !!quench valve!! but from reading what brain has posted isnt that basically what a liquid injection valve in some applications does in order to decrease the superheat at the compressor.
    ---- -- Yep -----

    http://www.corp.carrier.com/StaticFi...nuals/T319.pdf

    See page 13
    Last edited by Brian_UK; 19-12-2011 at 11:46 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: A quench valve ?

    I have come across the terminology as an in-line desuperheater / intercooler on two stage ammonia plants.