Results 1 to 3 of 3
  1. #1
    Join Date
    Aug 2010
    Location
    Australia
    Posts
    8
    Rep Power
    0

    Brema VM1700 Defrost not working



    Got a Brema VM1700 that runs a good freeze cycle then switches to harvest. The hot gas valve opens and hot gas travels a good way down the piping but doesn't seem to make it all the way through to the evaporator plates. Since the thermostat never gets to +8C the defrost cycle runs forever. Ice cubes remain stuck or eventually fall out but takes forever. The valve is opening, but gas isn't getting through properly. Any suggestions?



  2. #2
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    Re: Brema VM1700 Defrost not working

    check the gas charge, weigh in correct charge? Is the ice ice getting to thick? is the water fill solenoid working?

  3. #3
    Join Date
    Aug 2010
    Location
    Australia
    Posts
    8
    Rep Power
    0

    Re: Brema VM1700 Defrost not working

    Quote Originally Posted by savoc View Post
    check the gas charge, weigh in correct charge? Is the ice ice getting to thick? is the water fill solenoid working?
    yes, yes, no, yes.

    Turns out the hot gas valve diaphragm had developed a sticking point so while the valve was being commanded to open, and it did open, it was only opening a little bit.

    Just stripping the HGV internals out now (saves having to braze a new valve body in and the space is tight) so should have the monster working again soon).

    BTW thanks to the guys at Icemaster in Melbourne again for all the help.