    Dunnair ducted problems please help



    I have 1 Dunnair split Ducted AC that keeps tripping out on head pressure, It will only trip very occassionaly and not necessarily on hot days.

    System is single stage R22 with Externaly equalised TXV.
    when I am on site i cannot find a problem with the unit

    Suction pressure is 439KPA 63PSI
    Liquid Line pressure is 669KPA 97PSI
    Disharge Pressure is 200PSI
    superheat is 9.5 Celcius 17 degrees Farenheight
    liquid Line temp at exit of condensor is 16 degress Celcius 60.6 farenheight
    ambient temp is 28 degrees celcius
    Room temp is 22.5 Degrees
    Compressor Amps are L1 14.3A L2 13A L3 13.6A
    Compressor Voltage is L1 256V L2 256V L3 256V
    Condensor TD is 8.4Degrees Celcius

    Any help would be appreciated as i cannot solve this problem.

    Thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Dunnair ducted problems please help

    Is this unit cooling only or is it a heat pump?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    37
    Posts
    9
    Rep Power
    0

    Re: Dunnair ducted problems please help

    Its a heat pump unit but is doing it while cooling

  4. #4
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Dunnair ducted problems please help

    Hello
    I had a similar problem where at 27 degc ac units would cut out. they were slightly overcharged. and the hp/lp on those units might not be set right. set them correctly using your gauges and nitrogen.

  5. #5
    Join Date
    Feb 2008
    Location
    sydney
    Age
    52
    Posts
    32
    Rep Power
    0

    Re: Dunnair ducted problems please help

    you must be taking liquid line temp and pressure after metering device!

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Dunnair ducted problems please help

    Hi
    i think Brian was pointing you in the wright direction,possible fast change from cooling to heating,and viceversa could cause this hp cut out,
    i would also check as mentioned your presostats ,and condenser fans.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!