    Electronic Exp. Valve problem



    Hi all
    System is Freezer
    I have a problem about electronic exp valve.
    I have 2 x Refcomp 80 Hp ( parallel system)
    2 x Evaporater
    2 x sporlan Xev 22 Driver
    2 x Sporlan SEI 30 Expansion valve

    I am trying to control Exp. Valves with Superheat.
    But when the suction line getting closer the 0.50 - 0.60 bar
    expansion valve start to close and system getting stops (because suction getting 0.1 bar)

    Now I set minimun close persentages to %28 and solve the problem but. It is not a good solution.

    I can't understand the reason.
    Do you have any idea ?



  2. #2
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Electronic Exp. Valve problem

    i understand the problem my pressure sensor is 0.5 -11 bar. İ need to change it with 0 -12 bar and probably solve the problem

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Electronic Exp. Valve problem

    Try faulty EXV solenoid.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Electronic Exp. Valve problem

    Hi
    i would make sure the exv was chosen with the correct mop,if this exv is "big" on the system ,
    then your solution for immediet remedy is correct.or possibly as you replied the pressure transducer!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Electronic Exp. Valve problem

    Thanks all
    I solve the problem finally.
    I change the temp. probe and everything is cool =)

  6. #6
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Electronic Exp. Valve problem

    Room temp is -35c
    İ set the superheat 6
    What is the correct superheat and why ?