Thread: Electronic Exp. Valve problem
18-11-2011, 07:50 AM #1
Hi all
System is Freezer
I have a problem about electronic exp valve.
I have 2 x Refcomp 80 Hp ( parallel system)
2 x Evaporater
2 x sporlan Xev 22 Driver
2 x Sporlan SEI 30 Expansion valve
I am trying to control Exp. Valves with Superheat.
But when the suction line getting closer the 0.50 - 0.60 bar
expansion valve start to close and system getting stops (because suction getting 0.1 bar)
Now I set minimun close persentages to %28 and solve the problem but. It is not a good solution.
I can't understand the reason.
Do you have any idea ?
18-11-2011, 09:30 AM #2
Re: Electronic Exp. Valve problem
i understand the problem my pressure sensor is 0.5 -11 bar. İ need to change it with 0 -12 bar and probably solve the problem
18-11-2011, 10:08 AM #3
Try faulty EXV solenoid.
18-11-2011, 01:38 PM #4
i would make sure the exv was chosen with the correct mop,if this exv is "big" on the system ,
then your solution for immediet remedy is correct.or possibly as you replied the pressure transducer!
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
20-11-2011, 10:32 PM #5
Thanks all
I solve the problem finally.
I change the temp. probe and everything is cool =)
21-11-2011, 10:48 AM #6
Room temp is -35c
İ set the superheat 6
What is the correct superheat and why ?
Thanks for all