    hello every one
    Please help me, I need principle diagram of REFRIGERANT RECOVERY SYSTEM. how the oil filter works? how can i dispose of acid and base from refrigerant?
    thank you in advance.
  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Re: please help me with REFRIGERANT RECOVERY SYSTEM
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47
    Brian.
    You are a star!!!!
    That web page has Melsec FX connection cables.
    I thought they had become extinct years ago.
    Thanks Grizzly.
    Khong.
    I would assume that your only option is to recover the refrigerant, change the oil.
    Fit new filters and periodically change oil, filters as necessary.
    Using an acid test kit to check for acid concentrations left in system.
    Reclaiming and reusing the refrigerant is usually a very specialist job.
    No doubt someone may come up with a clean up method for the desperate?
    Grizzly
  4. #4
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15
    I used to have a "reclaimer" and that was exactly how it worked! It was configured with removable core filters and an oil seperator. The problem was we had no way of knowing when the refrigerant was "pure" enough to be reused, a bit of a guessing game and no one was really willing to take the chance of contaminating a system, refrigerants were still realatively inexpensive and so we really never used it. We no longer have the machine but if you had a way to verify the purity of the product I don't see why you cant "reclaim" refrigerant.
  5. #5
    Join Date
    Oct 2010
    Location
    thu duc
    Age
    34
    Posts
    28
    Rep Power
    0
    Quote Originally Posted by Brian_UK View Post
    thank you very much!