    30hxc carrier tripping on HP



    Hi all chiller guys.Got problem with a 30hxc carrier that continuously tripping on hp as soon as ambient temp reach 30dc.The following reading was taken yesterday.

    condenser water in 24.5 dc
    Condenser water out 28dc
    Lp.400kpa
    HP.trip at 1400kpa
    On standby pressure as soon as it trip both pressure equalise to each other at 600 kpa each hp/Lp.The system run only for 15 second only.And both system is flashing as well.Is there a way to check if the exv is operating correctly.And how can i put the system on 100% capacity to check if its undercharge.Help needed guys.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47

    Re: 30hxc carrier tripping on HP

    Hi Ironmen.
    Just a thought, Have you been able to measure the pressure drop across the condenser.
    Only the TD, seems High to me!
    Your HP is way high at 55c relative so I would be looking for poor flow through the condenser.
    With an undercharged system I would not expect to see a hp situation.
    But yes you are correct your expansion valve could be faulty and staying shut.
    Also is there any way Air could of gotten into your system? ( or nitrogen!)

    1 thing at a time I suppose.

    Grizzly
    Last edited by Grizzly; 29-10-2011 at 09:34 AM.

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 30hxc carrier tripping on HP

    If EXV was faulty you would get low sst trips, as grizzly said check your water flow

  4. #4
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: 30hxc carrier tripping on HP

    Hi guys.Im gonna do couple of test and i will let you khow the outcome.thanks

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 30hxc carrier tripping on HP

    Hi james
    if i remember correctly, at startup there is a delay on sst trip,
    so if system trips after 15 sec ,i would go with grizzly's direction!
    could be water flow,could be exv,
    lets here from the ironman
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 30hxc carrier tripping on HP

    What I mean is if the EXV was faulty the unit would indeed run in overide until it timed out and
    Trips on low sst, so I my mind the EXV can be ruled out unless it is completely jammed shut which I have never come across on a carrier EXV, but there is a first time for everything, also if the EXV is faulty there would more than likely be oil issues

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: 30hxc carrier tripping on HP

    With a constant tripping on HP at high ambient s makes me think that the rejected heat from the condenser is not being rejected properly. What is the condenser water flow rate and what is the chiller capacity?

  8. #8
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    39
    Posts
    69
    Rep Power
    15

    Re: 30hxc carrier tripping on HP

    i agree with above, sounds like a water flow issue.... maybe check strainers?

  9. #9
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    24

    Re: 30hxc carrier tripping on HP

    The discharge pressure is at 1400 kpa which is causing a trip on high pressure override and not hp switch.
    Check the condense water side All symptoms point to lack of water flow

  10. #10
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 30hxc carrier tripping on HP

    Hi
    lets here from the ironman !
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  11. #11
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: 30hxc carrier tripping on HP

    Ok guys,here we go.pull the cooling tower apart and found about six nozzle clogged up and there was very lack of water pressure and flow going through and found the bottom filter fully blocked.so unblocked all nozzle and clean the filter and test run still trip.
    And then the miracle ,temporaly bypass the plate heat exchanger and run the tower and ive never seen that tower working at full capacity,it was unbelivable.Start up the chiller and evrything was sweet as.All working perfect and both compressor working at full capacity.
    condenser Inlet water temp 24.5 dc
    Condenser outlet temp 31 dc
    Ambient 39 dc
    Hp 800 to 1000 kpa constant
    Its a big relief to get that system up and runing now i need to get that plate exchanger clean out and reconnect the outlet pipe from the condenser to its original location on the exchanger.And get a proper maintenance schedule and water treatment for that system.
    Thank you guys for all your support and help on that one apriciate it.

  12. #12
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 30hxc carrier tripping on HP

    Glad to hear you got it sorted Ironmen, always nice to hear feedback.

  13. #13
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 30hxc carrier tripping on HP

    Hi
    as james10 put it ,it is actully nice to get feedback,interesting too.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!