Thread: Thermocold chiller alarm
-
04-11-2011, 03:55 PM #1
Thermocold chiller alarm
Hi.
I have a problem with chiller AWA ANERSAVE II 2260 ZC NT SE B R407c.
There is alarm "main fun/pump maintenance hour meter" wich I try to acknowledge but it appear again. The hour meter is 10013 hours. I can`t find any information in manual.
Is anybody know how to acknowledge this alarm?
-
04-11-2011, 10:34 PM #2
Re: Thermocold chiller alarm
Never had an alarm from my fun pump
Sorry couldn't resist
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
04-11-2011, 10:38 PM #3
Re: Thermocold chiller alarm
The run hour threshold is set for 10,000 hours, you need to reset the run hours.
Unfortunately I'm not familiar with these chillers.
What make is the controller on it??
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
05-11-2011, 03:55 PM #4
Re: Thermocold chiller alarm
The reset in the maintenance branch of the microprocessor.
Enter with service password and reset hour counter.
-
05-11-2011, 04:39 PM #5
Re: Thermocold chiller alarm
Hi
if it is a carel pco controller,
you indeed need to go to the maitenence menu and reset it there.
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
07-11-2011, 09:49 AM #6
-
07-11-2011, 11:24 AM #7
Re: Thermocold chiller alarm
The problem has solved.
The password is 1234.
Thanks to "stufus", "goshen" and "NoNickName"
-
07-11-2011, 01:34 PM #8
Re: Thermocold chiller alarm
Glad to hear it..
Cheers