    hot water coils.
    Hi chaps
    Currently in discussion with a guy regarding his hot water battery on his York package unit(supply side) . In the spec it says "hot water re-heat battery" and design is inlet 16c off 21.C
    I have told him that the battery is too small to be considered a space heater and as such he should be using his rads more.. He suggests that isn't right and it should also heat the rooms. Can anyone confirm my line of thinking
    ireland
    1,451
    Re: hot water coils.
    Richard
    Is the York a heat pump? I have a pub that has a heatpump plus a rad literally in the supply duct, as the york can't supply enough heat on its own. if it's classed as a reheat then it sounds like a close control, controlling humidity?
    al
    Let's be honest, with an air off of 21°C it isn't going to provide much in the way of heating is it?
    That's assuming that the on temperature is at 16°C, any lower and he's lost it.
    70
    4,702
    47
    RB.
    Do you have any model No's to reference against?
    Although I tend to agree with you and Brian.
    "Silk Purse out of a Sow's ear springs to mind.
    Oct 2008
    newbury
    1,444
    just looked at the label. Seems to be straight cooling with no electric heat option fitted..DSC03440.jpg
    70
    4,702
    47
    A Strange one you have there RB.
    I have some old York paperwork and the best I can make out, is it is cooling only.
    With D1C meaning cooling (Mk1) model. I have assumed this from using the attached much later explanation.
    I suspect the Mk 1 is pre-pdf?
    ireland
    1,451
    That looks like an american made one, heater amps are listed though, are they not installed Richard?
    al
    Oct 2008
    newbury
    1,444
    Quote Originally Posted by al View Post
    al
    No difficult to see but if you look the x shows what heater is installed and the x is against none
    so it's a cooling only with no electric heaters and a small reheat hot water coil..