Is there another reason other than oxidation (rusting) of the piping internally and externally why ordinary steel (not stainless steel) is not used on Compressor rack piping operating on R22 refrigerant?
Steel pipe is a lot cheaper than Copper pipe, so why don't all the Compressor rack manufacturers use ordinary steel piping to keep costs down?
buddy
-
30-08-2011, 06:38 PM #2
Re: Supermarket Compressor racks/packs using steel piping?
How about impurities from the manufacturing process.
-
31-08-2011, 01:09 AM #3
Re: Supermarket Compressor racks/packs using steel piping?
Hi Emmett,
Do you mean impurities in the manufacturing process of the steel pipe itself or in the process of manufacturing the Compressor rack?buddy
-
31-08-2011, 11:19 AM #4
Re: Supermarket Compressor racks/packs using steel piping?
Frigrite in Australia used to manufacture racks with steel discharge headers up to the oil sep, they were a pain in the arse for comp changes as there was no flex in the piping to get 4 cylinder compressors out from under the piping. Bitzer manufacture racks in Australia with steel suction headers for R134a operation to comply with Australian standards. A lot of subcritical Co2 racks are built in steel and obviously b nearly all of transcritical ones.
...and she said "give it to me you big fridgie"
-
31-08-2011, 01:40 PM #5
Re: Supermarket Compressor racks/packs using steel piping?
Hi 750 Valve,
Thanks for your input.
I have seen many different compressor racks/Packs with partial steel piping used as you mention in your post.
Still, I have come across 2 Compressor racks (1 LT and 1 MT) operating on R22 refrigerant and ALL the piping is steel, suction and discharge piping/headers etc etc, not 1 piece of copper piping is to be seen anywhere?
(These racks are approx 6 years old).
It just got me thinking why do compressor rack manufacturers use copper if it so expensive instead of steel and there is no technical reason not to use steel?
Surely if they used steel they would have a competitive edge on pricing?
I was hoping someone on RE forums may have a technical answer for not using steel piping with R22 refrigerant compressor racks?
I love your avatar (-:
best regards
Buddy.buddy
-
31-08-2011, 02:30 PM #6
Re: Supermarket Compressor racks/packs using steel piping?
Yes, Cooper is a lot of expensive, specially for big diameters.
Cooper pipes are better to make the pipelines, because welds are easier and cleaner (good for the internal circuit)...so you shall count with a reduction on the connection mounting hours (less labor).
Also lower tendency for corrosion » less leaks.
Don't need to paint the cooper pipe.To make progress is never good enough, I want to do better and better and better
-
31-08-2011, 02:43 PM #7
-
31-08-2011, 05:42 PM #8
Re: Supermarket Compressor racks/packs using steel piping?
Hi Emmett,
Your point would stand up regarding labour costs in Western Country's with high labour costs.
However plenty of compressor packs/racks are manufactured in low labour cost country,s such as China, Linde (Carrier), Heatcraft, Hussmann etc all manufacture compressor racks in China, but they all still use copper piping which is very expensive even in China in comparison to steel.
So sorry I don't see the validity of labour costs being the issue for preventing steel being used on all compressor rack piping?
Is it just a historical thing that, that's the way they have always manufactured compressor pack piping in copper?
I,d love someone to come up with a technical reason for not using steel piping.
best regardsbuddy
-
01-09-2011, 08:54 AM #9
Re: Supermarket Compressor racks/packs using steel piping?
To make progress is never good enough, I want to do better and better and better
-
01-09-2011, 12:37 PM #10
Re: Supermarket Compressor racks/packs using steel piping?
rusty drier core.jpgrust.jpgas you can see this is rust residue taken from a linde pack, as the receiver sits on an angle the liquid never sat in the top of the receiver and through time the inside of the steel receiver become rusty as hell which eventually saw the plant being repalced, linde reported back that the moisture/water in the system attacked all the welds used on the receiver which spread into the rest of the steel, so i suppose steel isnt that great!
-
03-09-2011, 04:52 PM #11
-
05-09-2011, 08:20 AM #12
Re: Supermarket Compressor racks/packs using steel piping?
Thanks Coolhibby1875 for the photos and information.
Have you any more?buddy
-
05-09-2011, 08:25 AM #13
Re: Supermarket Compressor racks/packs using steel piping?
Hi Mark,
Just wondering that refrigerant leaks and rust seems to coming up as the 2 common reasons why steel piping is not used on Supermarket Compressor racks instead of copper piping.
As regards leaks through steel piping is that maybe because it is more porous than copper or just bad welding (jointing) that Profroid stopped using steel?buddy
-
05-09-2011, 09:25 AM #14
Re: Supermarket Compressor racks/packs using steel piping?
If the World did not Suck, We would all fall off !
-
05-09-2011, 04:12 PM #15
Re: Supermarket Compressor racks/packs using steel piping?
Hi Chillerman2006,
Yes I should have put porous because of the leaks caused by steel rusting and not porous at the molecular level.
Thanks for pointing it out.
best regardsbuddy
-
05-09-2011, 09:26 PM #16
Re: Supermarket Compressor racks/packs using steel piping?
Hi Buddy
I should have realised what you meant mate ... was in a rush this morning ... got up late .. logged in for a quick browse & then made later still !
R's chillermanIf the World did not Suck, We would all fall off !
-
07-09-2011, 01:46 AM #17
-
07-09-2011, 01:49 AM #18
Re: Supermarket Compressor racks/packs using steel piping?
So folks it looks like from comments on the thread, the only reason is that steel piping is not used on Supermarket Compressor racks is because steels rusts if moisture gets inside the refrigeration system.
Is that the only reason?
best regards.buddy
-
07-09-2011, 03:13 AM #19
Re: Supermarket Compressor racks/packs using steel piping?
Hi Buddy
generally steel pipe is factory fitted with a mill scale residue and surface rust even if capped that has to be removed, here steel welding by regulation is by certified welders, cutting and grinding and welding adds more gunge to system. With R22, a really good flushing cleaning refrigerant all the crap ends up back at compressors and suction strainers etc., commissioning is a big drama getting systems clean. Stainless steel less of a problem, copper better again if done properly with nitrogen purging.
-
07-09-2011, 08:50 AM #20
Re: Supermarket Compressor racks/packs using steel piping?
To make progress is never good enough, I want to do better and better and better
-
07-09-2011, 08:51 AM #21
Re: Supermarket Compressor racks/packs using steel piping?
I meant thick wall not tick wall
To make progress is never good enough, I want to do better and better and better
-
12-09-2011, 03:11 AM #22
Re: Supermarket Compressor racks/packs using steel piping?
Thanks every body for your input.
So in conclusion to my question it looks like the majority of you say corrosion is the no1 reason for compressor rack manufacturers not using steel piping on compressor racks.
best regardsbuddy
-
17-09-2011, 11:29 AM #23
Re: Supermarket Compressor racks/packs using steel piping?
One reason assigned is the loss of ductility of ordinary steel ( mild steel) at lower temperatures
below (-40) deg c ..........
-
18-09-2011, 12:55 PM #24
Re: Supermarket Compressor racks/packs using steel piping?
Hi D.D,
Yes I understand the ductility issue at low temperatures but the lowest evap temp I have come across for Supermarket application is for Island freezer system at -35 degrees C so that would not be a problem?Ibuddy
-
18-09-2011, 02:00 PM #25
Re: Supermarket Compressor racks/packs using steel piping?
would you not also have the battery principal as well copper steel and a acidic liquid = slight voltage just a thought