Page 1 of 3 123 LastLast
Results 1 to 50 of 135
    Jun 2007
    At sea
    367
    How to assign thermodynamic properties after splitting two phase into gas and liquid
    Looking at a simple TXV system. Lets assume after the TXV we seperate the gas down one pipe and the liquid down another. The question is how do we assign the correct thermodynamic properties to each fluid when it gets to end of its pipe.
    The gas we want to do work on like heat it or compress it but before we can see where it ends up and predict its temperature and pressure we need to know from where we started? So do we move the gas out of the middle of the bell on a PH diagram to its edge and similarly do we move the liquid back to the saturated liquid line to gets its new properties?
    Simply jumping out of the bell interior means that the enthalpy and entropy both make huge changes without any process being done. Hmmm
    Your thoughts welcome
    Chef
    Apr 2006
    55
    1,908
    30
    Re: How to assign thermodynamic properties after splitting two phase into gas and liq
    Quote Originally Posted by Chef View Post
    Chef
    Gents, to save time & make ease of reading, Jump to; # 103
    Just drop the txv & sounds like flooded plate heat exchangers with low pressure vessel, chilled water system, if you plot that on a chart it will come back as you described,
    (other than that I am lost for what your trying to acheive)
    The liquid remains in the heat exchangers, with some in the vessel, then the boiled of vapour is piped from the top of the vessel back to compressor
    You can not get much work out of the vapour compared to the liquid, transfered to vapour
    What are we trying to acheive ?
    R's chillerman
    manchester
    5,639
    i posed that question to "ask jeeves.com"(other similar sites are available)and the reply was-if u chop out the tev then each seperated pipe is going to p*ss out refrigerant.
    Apr 2006
    55
    1,908
    30
    I dont know for sure, you can not believe everything you hear on the net, (as tex found out) just asked the mrs though & she has confirmed "you would loose the gas & some oil"
    Jun 2007
    At sea
    367
    Quote Originally Posted by chillerman2006 View Post
    R's chillerman
    So I split the gas and liquid but what h and s values are then given to each seperate flow. In a simple example lets have the evap at 1 bar and x=0.3
    The gas/liquid is at h=231 and s=1.13 but now rip away the gas and suddenly it has a value of h=384 and an s=1.75 but we have not done anything except seperate the flows and we see a huge change in properties?
    This means the gas/liquid together has one set of properties but when seperated they both have differant set of properties. What are the rules for reassigning the properties to each of the seperate streams.
    Simply I want to know where to plot the 2 seperate streams on a PH diagram.
    Chef
    install monkey - seems Jeeves is way up to speed on this topic eh!
    Apr 2006
    55
    1,908
    30
    Chef
    chef
    I am struggling here with what you mean & what your trying to achieve
    As far as plotting the cycle on a chart, your vapour is to the right, your saturated vapour is in the middle & the liquid is to the left
    but I cant see how this can be plotted without combining temperatures with pressure or why you would want to do this
    Apr 2006
    55
    1,908
    30
    A system needs to be balanced and an equilibrium from the energy transfering into an evaporator needs to balance out with the energy leaving the condensor, if you remove all vapour, what are we doing pumping neat liquid round a system (& as you mentioned) no work is being done
    Apr 2006
    55
    1,908
    30
    Energy can niether be created or destroyed just transfered from one form to another, with this in mind and my previous posts combined
    The wheel has been created and the rules of thermodynamics are set in stone
    My question is what are we trying to acheive ? (the impossible)
    I dont understand
    Apr 2006
    55
    1,908
    30
    Come on chef
    not many are like me & dont care what others think !
    am not at this level, not at design level even
    and do not see what benefit it is
    this could be here a while as 60+ views already & nobody has a clue
    Aug 2009
    New Zealand
    2,554
    Hi Chef, good to see you are looking into our little problem.
    As far as enthalpy goes, if the vapor is just that vapour (full seperation) then the enthalpy will be on the saturation point of the curve. But how is entropy effected.???????
    Aug 2009
    New Zealand
    2,554
    Come on chef
    The question is not based upon what you would expect!
    Apr 2006
    55
    1,908
    30
    Well chef
    I could repeat all of what I have now been told & pretend I fully understand
    But I have to work through some of it
    I'll let you know I have been put on the right track though
    utilizing the flash gas potential for generating flow through an evaporator
    gaining maximum velocity through the evap coil which makes it 1 to 1 efficient
    r's chillerman
    Aug 2009
    New Zealand
    2,554
    well chef
    i could repeat all of what i have now been told & pretend i fully understand
    but i have to work through some of it
    i'll let you know i have been put on the right track though
    r's chillerman
    ---------no--------
    Apr 2006
    55
    1,908
    30
    Well Mr Chef
    I shall thank you for bringing this to my attention
    I have and will continue to gain from this
    As I said earlier I am not at this level
    But will be following the progress & eagerly await the outcome
    To see what can be acheived at such a level, I am yet to fully understand
    And thankyou Mad for setting me straight, I can sleep now today
    Good night Gents
    Apr 2006
    55
    1,908
    30
    Mad
    Maybe 4:00 here, I'm not sleeping till I have exhausted my understanding or lack of
    Trying to understand here full seperation
    And by this I mean on the chart the point of seperation I can see
    With (as you said) enthalpy following the curve of saturation/vapour
    enthalpy tails off at the point of the opposite curve saturation/liquid
    So (correct me) this point where enthalpy tails of is the point of entropy
    The point of diss-order prior to order and the point at which you need to achieve full seperation
    If this is correct, how do you physically get to this point to acheive seperation in the first place ?
    And how would this be put to use ?
    What sort of system (design) if possible to get to this point & what would this acheive ?
    Aug 2009
    New Zealand
    2,554
    Firstly read the first question, there is no mention of an evaporator.
    So without thinking any further than what I say next
    We have an open flash economiser vessel, liquid in, liquid out vapour out. what are the properties of all. Are there any strange things happening???
    Apr 2006
    55
    1,908
    30
    There is no stage of saturation
    Aug 2009
    New Zealand
    2,554
    Apr 2006
    55
    1,908
    30
    No there must be (surely) a point of saturation, just this is somehow minimal as you have found a way for full seperation
    Aug 2009
    New Zealand
    2,554
    Yes seperation is an issue, but not the issue in hand (it must happen in an open flash vessel anyway) We are onlt talking about internal energy, (law of conservation)
    Apr 2006
    55
    1,908
    30
    There is stage of saturation, the point of entropy, where diss order becomes order once more , the point at which you achieve full seperation ??
    Apr 2006
    55
    1,908
    30
    I am following I am just trying to work out where we are tranfering the energy from and to - to enable enough to achieve this full seperation
  23. #23
    Aug 2009
    New Zealand
    2,554
    high pressre liquid in (from cond) reduce pressure, what happens?
  24. #24
    Apr 2006
    55
    1,908
    30
    The liquid entering the flash econimiser has a specific heat/energy & at the point of seperation you are transfering the heat/energy from the liquid into the vapour, in effect subcooling the liquid
  25. #25
    Aug 2009
    New Zealand
    2,554
    Not quite, apart from liquid head there is no sub cooling, and you are converting some liquid into vapour to keep the energy balanced. What then are actual properties of each exit stream. This is the question in hand?
  26. #26
    Apr 2006
    55
    1,908
    30
    The liquid entering the flash econimiser has a specific heat/energy by flashing of some lquid into vapour, you lower the pressure/temperature of the remaining liquid transfering the heat/energy to the vapour, subcooling the remaining liquid...
  27. #27
    Aug 2009
    New Zealand
    2,554
    You are cooling the liquid by vapourizing, the pressure has dropped, so the liquid is at saturation, hence is not sub cooled.
  28. #28
    Apr 2006
    55
    1,908
    30
    Liquid in - saturated liquid
    liquid out - liquid only
    vapour out - vapour only
    neither are superheated or subcooled
    & therefore
    to go back to the question from Chef - #5
    They would both be plotted on a ph chart along their respective lines at the point of saturation
  29. #29
    Aug 2009
    New Zealand
    2,554
    & therefore
    Yes one would think so?????, unless someone can show something else??? and this is all chef was asking
  30. #30
    Apr 2006
    55
    1,908
    30
    Thanks Mad
    I understand what you mean at last
    Talk about - I beat around every bush first & need spoon feeding
    Thanks Chef, if you had not have posted that question, there would still be that gap in my knowledge
    (But scrolling back up - no-one else came along and attempted it did they)
    Back on track
    So what you's were looking for was not me butting in, but someone on par with yourselves, who maybe could have come up with that something else that may or may not be there ?
  31. #31
    Aug 2009
    New Zealand
    2,554
    no butting in is good, if you do not ask, then you will not get an answer. No one knows everything,
    " the more I know, more I know, I know nothing"
  32. #32
    Apr 2006
    55
    1,908
    30
    Yeah, thanks Mate
    Got a new signature too now
  33. #33
    Mar 2009
    KZN, South Africa
    64
    2,212
    The methodology for solution will very much depend on the two-phase model you select. Flow regime for two-phase flow can be rather interesting & the theory is far from settled.
    With different flow regimes, comes different levels of phase interaction.
    So, pick a suitable model, or models, predict the flow regime & determine the appropriate properties.
    I have a few very useful references to hand. If you pm me, with your current e-mail address, I'll get these onto you.
  34. #34
    Jun 2007
    At sea
    367
    Chillerman, Mad is right and the whole question is just about how to get the properties of the split streams. If I read the previous posts correctly it seems it should be possible to simply move the 2 streams to their respective lines on the bubble but does that meet the no work and no heat input criteria is met. So I propose this:- (which is way too complicated for a Sunday morning I should add)
    As no work or heat has been applied to either of the separated streams we can write the state function as
    dS=dQ-dW
    and the process as dh=dQ-dW+pdv+vdp
    As dQ the heat input is zero and dW the work done is zero the dS must be zero
    So x*S4-S3+S5-x*S5 = 0
    And as both p the pressure and v the volume are constant dh can be set to zero so there is no gain or loss of enthalpy
    So m*(h4-h3)-m*(1-x)*(h4-h5) = 0
    Where h3 is the enthalpy at a quality of x
    And h4 is the enthalpy at the gas line
    And h5 is the enthalpy at the liquid line
    Also S3, S4 and S5 are the entropy at the same locations.
    This boils down to the fact if these state functions are equal to zero then we can indeed split the gas out and position directly on the gas line whilst the liquid must then be plotted on the liquid line with the caveat that both streams must have their respective masses carried with them and new processes can then be started.
    But I am still mystified why the gas can have its entropy changed without work or heat input?
    Chef
  35. #35
    Jun 2007
    At sea
    367
    Quote Originally Posted by desA View Post
    Thanks for the offer of the 2 phase papers but we really need to get to the pure gas and liquid states and the 2 phase episode is already past. There seems to be very little referance to this problem where ever I have looked.
    Chef
  36. #36
    Apr 2006
    55
    1,908
    30
    dS=dQ-dW
    Chef
    Afternoon Chef
    Thanks for such a detailed answer to work with,
    (This is going to take me all day to get my head around as I have to reference all the letter symbols first, before i can attempt to work out what you mean.)
    Morning MF
    But I will, you's have me hooked now.
    side tracking slightly away from the original reason for posting as i always look at the final acheivement
    the research that you's are doing is for the design of 'A'
    the problem i have is where they (liquid/vapour) end up and thus system balanceing
    the component that does the system work has a limited ability
    with this in mind
    the more work it does removing the vapour from 'A'
    the less work it can do in the usual way
    ideally the liquid will be subcooled before it leaves 'A' moving it away from the bell
    but it appears to me that this will reduce overall system ability to cool
    and there is a fine line of how much vapour can be removed from 'A' without this reduction
    I know you's must have already considered this so,
    Just asking, can enough vapour be removed from the liquid to increase cooling without loosing cooling ability in the conventional way ?
  37. #37
    Aug 2009
    New Zealand
    2,554
    Chef is in Fiji (Lucky bar stewerd), would I be working on refrigeration fomulures, or sucking dowm a Pina Colarda?
    Good on chef for making the wrong choice.
    CM, this not the process only the very beginning
  38. #38
    Apr 2006
    55
    1,908
    30
    Bar Steward,
    When your hooked on info/solutions - yes the right choice!
    All I could think of last night during dinner - when most would be thinking of serviceing
    Oh well I will have to wait until your in a position to safely reveal
    Am even more entreagued now - as i was thinking it could only be in one position on a conventional system, obviously much more to it,
    Hope it all goes well next month
  39. #39
    Jun 2007
    At sea
    367
    Your were right Mad and so we went to the sun deck and had a couple of Fiji Golds and the watched the world cup final and saw Brazil win 3 - 2. Exemplorary. Good input.
    So the last test seems to be that h5-h3-x(h5+h4)+2xh3 must tend to zero to make
    dh=d(S+pv) true.
    But for this to happen it makes it an isochoric process and that then means that the gas portion at the outlet of the TXV already has the properties of the gas at the gas line. It is therefore only the liquid that holds the core thermodynamic properties. ie it does not matter what you do with the gas as it cannot affect the liquid except for normalising the mass if one removes it. Interesting!
    How to calculate this on the fly and use it is a distant goal at the moment. But without it how can we go to stage 2.
    Knickers, we are going back to the sun deck for some more Fiji Gold.
    Chef
  40. #40
    Aug 2009
    New Zealand
    2,554
    World cup???? Brazil???? Soccer???? (surely not that far behind the times????????)
    Golds! yummmmmmmmmmmmm!
    So it would seem that all we need to know at this point, is the % by mass of the lquid and vapour streams at the relevent saturation points?
  41. #41
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    Thanks Mad
    Back on track
    Have to chime in here, potential rant warning, and don't take it personally, but owning up to the fact that i've had to fight for every advancement in knowledge gained to date to succeed, not only in the refrigeration industry, as my main focus, but in my other curricular studies or hobbies i call them, including psychology and non mainstream medical advancements, that i struggle to digest the "quantum" aspect of this thread.. So continue, (giving the Jedi hand movement), and i will follow this thread through without asking questions and absorb what i can as it does trigger curiosity. Thanks "Mad" and C.M... Mike.
  42. #42
    Mar 2009
    KZN, South Africa
    64
    2,212
    Annular flow, slug flow, plug flow - all have vapour split from liquid. Take your pick.
    You will need to understand the flow regime at some point, I fear. Thermodynamics will have assumptions about the fluid under consideration. Your final system will be somewhere between two extreme positions, due to liquid-vapour interaction.
  43. #43
    Apr 2006
    55
    1,908
    30
    Quote Originally Posted by mikeref View Post
    Good Evening Mike
    You'll notice I did no contribution here mate, Have just found more I want to learn & comments keep the post up there, which may lead to another view from someone at their level
  44. #44
    Jun 2007
    At sea
    367
    It is the under 20 world cup held in Columbia and was live today.
    I will work on the other stuff later.
  45. #45
    Apr 2006
    55
    1,908
    30
    Evening Chef
    @ nearly 7pm more work, on a sunday, you must be due a few drinks now !
  46. #46
    Aug 2009
    New Zealand
    2,554
    Hi Mike, please ask questions! As design engineers it is very easy to get an idea into our heads, and very difficult to remove. Hence the questions do seem to be vague, as we are looking for a different approach or answer. So please jump in as this can also help us re think our thoughts. What I am looking for is for proof that the widget will not work. or reversly that the widget may work.
  47. #47
    Oct 2003
    5,630
    Just noticed now this post. I thought if Chef's asking a question and scrolling down, Mad Fridgie replies to it, then I have to read ever comma of this thread because both of them will dig very deep in the Thermodynamic laws again. Which I will do right now...reading, not digging.
  48. #48
    Aug 2009
    New Zealand
    2,554
    Would the flow regime relate directly to the exit of the expansion valve and its effects reduce if the bell (liquid vapour seperator) is a reduced velocity and impegement type. (basically allowing the heavy liquid to fall to the bottom and the lighter vapour to rise to the top)
  49. #49
    Aug 2009
    New Zealand
    2,554
    I am certainly not at the level chef, DesA or Peter, just a different level. I am always learning from these guys,(thank you), If you are unsure of what is being said. ask!, and no doubt we will try to answer in a different termonology.
  50. #50
    Oct 2003
    5,630
    Come on chef
    This quote stands!!