Results 1 to 18 of 18
Thread: carrier 30gx
    May 2008
    uae
    44
    40
    carrier 30gx
    pls help to fix this alarm in carrier 30gx chiller
    alarm # 62
    this alarm is coming will start up only after reseting one or two times compressor starts working normal.
    70
    4,702
    47
    Re: carrier 30gx
    Anish
    Refer to the attached.
    When did you last service your comp.
    Suspect oil and or oil filter issues.
    May 2008
    uae
    44
    40
    Re: carrier 30gx
    hi
    we have not serviced the compressor.
    we have changed 6 months before compressor oil and external oil filters.
    70
    4,702
    47
    Re: carrier 30gx
    Ah!
    External oil filters!
    What about the internal?
    May 2008
    uae
    44
    40
    Re: carrier 30gx
    hi
    we have not tryed that (internal oil filters)
    pls advice the procedure for that.
    Apr 2009
    israel
    778
    Re: carrier 30gx
    you need a 19 mm alan key ,
    pump down the unit ,change filter ,and back to normal operation!
    good luck
    70
    4,702
    47
    Re: carrier 30gx
    Sorry for not replying this morning only I was on my way out the door to work.
    Anyway as Goshen suggests change the internal Oil Filter.
    Follow the link below to an earlier post regarding Internal oil filters.
    http://www.refrigeration-engineer.co...er+Oil+filters
    Good Luck,
    Also read the attached.
    May 2008
    uae
    44
    40
    Re: carrier 30gx
    it is possible to pump down this unit if so how
    Apr 2006
    55
    1,908
    30
    Re: carrier 30gx
    Quote Originally Posted by anish View Post
    If your not sure about pumping it down (i dont know the unit) then just isolate (power + valves) the compressor and use your transfer pump (reclaim unit) to pump the refrigerant into the high side
    manchester
    5,639
    Re: carrier 30gx
    looks like someones after a foriegner,(work) theres not many horses in uae more camels!! oh and an arab who's stood with his finger up his a**e wondering have i pumped it down correctly -you should be able to spot him at the airport-hell have facial burns and a white stick, dont give him any passwords jesus.
    Apr 2006
    55
    1,908
    30
    Re: carrier 30gx
    give him passwords
    Hi Install,
    seems a bit of a risk to me, but if you insist !
    As one of the other members was looking for work the other day, in a nice warm place
    passwords attached,
    R's chillerman
    Attached Files Attached Files
    Jun 2009
    North East England
    712
    Re: carrier 30gx
    Quote Originally Posted by goshen View Post
    good luck
    You should NOT pump down these machines, as they have a permanent live to the compressor and if a vacuum is pulled can cause the compressor to go to earth.
    to change internal oil filters isolate oil valves on the oil seporator, connect a 1/4" hose to the compressor scrhrader located next to the oil solenoid and recover the oil into a suitable container there should only 50ml of oil max that comes out. then using a 19mm allen key remove the filter cap above the compressor discharge line and GENTLY remove the old filter DO NOT twist it as they can snap and if this happens it is difficult to remove.
    HOWEVER this is only applicable to phase 2 and 3 machines ( black or grey prodialog control) if the unit has a HSIO controll this is a phase 1
    machine in which case you will need to recover the entire charge of refrigerant then change the filter
    May 2008
    uae
    44
    40
    Re: carrier 30gx
    hi
    thank u all for ur valuable suggestions.
    we ordered the filter already.
    i will be back to u once its finished.
    Apr 2006
    55
    1,908
    30
    Re: carrier 30gx
    Off topic - needed removing
    manchester
    5,639
    Re: carrier 30gx
    Gotcha!!! Haha
    Quote Originally Posted by chillerman2006 View Post
    Hi Install,
    passwords attached,
    R's chillerman
    Apr 2006
    55
    1,908
    30
    Re: carrier 30gx
    Gotcha!!! Haha
    Maybe, Maybe NOT !
    I created this doc & maybe this means I have proprietry Rights, Only one here I know that can confirm this for sure Is 'Abe'
    Feel free to bring it to his attention for clarification
    R's CM
    May 2008
    uae
    44
    40
    Re: carrier 30gx
    hi
    Replaced oil filter succesfuly and unit running good.
    During the job there was some amount of gas passing from filter opening.
    We Isolated all the valves and oil solid valve also.
    How can this be prevented.
    As we are planing to fix other units also.
    Jun 2009
    North East England
    712
    Re: carrier 30gx
    Refer to my earlier post some units require the gas removing, please don't ask for advice if your not going to follow it!!!