R600a refrigerant system.
Hey guys, if i going to design a refrigeration system using R600a, how do i calculate all those ,length and size for capillary tube and condenser if i already had the spec for compressor and evaporator?
-
14-08-2011, 03:03 AM #2
Re: R600a refrigerant system.
Please Help!!!
-
14-08-2011, 01:33 PM #3
Re: R600a refrigerant system.
Would this be any help?
http://www.danfoss.com/businessareas...ils/dancap.htm
I fix them not make them so wouldn't have a clue personally how to size a cap tube.
JonMostly found in Oxfordshire, UK :)
-
14-08-2011, 04:46 PM #4
Re: R600a refrigerant system.
thx a lot, but how about the condenser? any idea?
-
14-08-2011, 09:08 PM #5
Re: R600a refrigerant system.
I would think you need a condenser with the same or sligthly bigger heat rejection than your systems cooling load at the ambient temperature it will be running in.