    Arneg 2010 and 2011 Cases with failing liquid line sol valves



    Has anyone experienced problems with danfoss 3/8 10mm new style sol valve o ring failing between the brass base and stainless top section. We have had several fail on new and retrofit installation using 404a with eal 22 oil causing loss of refrigerant. Failure time is normally 3 to 6 months after installation. Exchanging the o ring solves the problem, problem may be over heating when installed at production?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Arneg 2010 and 2011 Cases with failing liquid line sol valves

    I've only had two of these leak, one was in the hot gas line on a Zanotti and i think it just got cooked during defrosts, the bolts were loose on the other one and it was fine once tightened.

    I don't do much Arneg style things though.

    Where do you get the new o rings from?

    Cheers Jon
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41

    Re: Arneg 2010 and 2011 Cases with failing liquid line sol valves

    Had a lot of these failures a few years ago, turned out installers never stripped or protected the valves before brazing, generally failed sooner than 3 months though.

    alec
    Mostly found in the southern part of this green and pleasant land.