    Clivet chiller fault



    Hi I have been called out to a fault on a clivet chiller model wsat-xsc120d
    The fault code is E213 and description is module not connected however this fault clears it self after about 5 mins but re-occurs 4 or 5 times a day.

    Please help me it's really frustrating as the chiller is run fine as I speak.

    Thanks

    Chiller



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Clivet chiller fault

    Sorry to ask , but is module (whatever that might be) connected?

  3. #3
    Chillere213's Avatar
    Chillere213 Guest

    Re: Clivet chiller fault

    I guess it is as the chiller runs normally most of the day, im not even sure where the module is ?

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Clivet chiller fault

    Modules are the boars I.e ap3 is compressor module, ap2 main control module and ap25 pump module.

    Do you mean 214 fault code because this Is module not connected?

    I think the 200 fault codes refer to the evaporator module.
    The difference between genius and stupidity is that genius has its limits.

    Marc