19-07-2011, 11:08 AM #1
Clivet chiller fault
Hi I have been called out to a fault on a clivet chiller model wsat-xsc120d
The fault code is E213 and description is module not connected however this fault clears it self after about 5 mins but re-occurs 4 or 5 times a day.
Please help me it's really frustrating as the chiller is run fine as I speak.
Thanks
Chiller
-
19-07-2011, 11:51 AM #2
Re: Clivet chiller fault
Sorry to ask , but is module (whatever that might be) connected?
-
19-07-2011, 03:24 PM #3
Re: Clivet chiller fault
I guess it is as the chiller runs normally most of the day, im not even sure where the module is ?
-
19-07-2011, 04:27 PM #4
Re: Clivet chiller fault
Modules are the boars I.e ap3 is compressor module, ap2 main control module and ap25 pump module.
Do you mean 214 fault code because this Is module not connected?
I think the 200 fault codes refer to the evaporator module.The difference between genius and stupidity is that genius has its limits.
Marc