    Question Daikin vrv seriously need help



    Need some serious help with an old Daikin vrv sytem. It's heat recover r22.

    Models of equipment:


    Function unit: Br3kjv1
    Rny10ky1r by 2
    Rxy10ky1r

    With 13 indoor units attached.

    The problem we are having is that the system won't load up on heating. System will run fine in cooling. Spoke to Daikin and replaced low pressure transducer. Fit service checker to system to check out door expansion valves were operation correctly all seem fine.

    System has bein pressure tested and evacuated down to 350 microns so I know there nothing wrong with charge. Inverter unit starts and brings on the other too but they only run for 5 mins before they unload. Coil temps only get up to 35 to 40 c.

    I have sent the service checker info to the Daikin europe head office and am waiting to hear back just taught someone else may have come across this prob.

    I was only on site to fit service checker another lad has bein there over a week now checking everything so if there is more info needed I can get it quick enough.

    Thanks in advance any new ideas would b great.



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin vrv seriously need help

    I know you say you vacced down to 350 microns so the vac is good but is the charge correct?

    I dont work on Daikin much so i may be wrong but after looking at the piping diagrams the obvious thing for me to check would be that the discharge solonoid is open and the 4 way rv arent stuck.

    What pressures are you getting? i.e is the discharge ramping up to target discharge pressure 25-28bar?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin vrv seriously need help

    Yes the charge is perfect. 64kg long pipe runs.

    The head pressure was up at 18 bar when I was on site. The service checker shows all valves are open correctly but I did question if there could b a mechanical problem with a valve and no show up on the service checker. I will ask the guy in site to check and post results. Thanks for the quick response.

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin vrv seriously need help

    Sorry i've just re-read my post 18bar seems normal doesnt it because it's on R22 not R410a
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin vrv seriously need help

    Yea that's cool taught it was just me

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin vrv seriously need help

    Quote Originally Posted by ktm View Post
    Need some serious help with an old Daikin vrv sytem. It's heat recover r22.

    Models of equipment:


    Function unit: Br3kjv1
    Rny10ky1r by 2
    Rxy10ky1r

    With 13 indoor units attached.

    The problem we are having is that the system won't load up on heating. System will run fine in cooling. Spoke to Daikin and replaced low pressure transducer. Fit service checker to system to check out door expansion valves were operation correctly all seem fine.

    System has bein pressure tested and evacuated down to 350 microns so I know there nothing wrong with charge. Inverter unit starts and brings on the other too but they only run for 5 mins before they unload. Coil temps only get up to 35 to 40 c.

    I have sent the service checker info to the Daikin europe head office and am waiting to hear back just taught someone else may have come across this prob.

    I was only on site to fit service checker another lad has bein there over a week now checking everything so if there is more info needed I can get it quick enough.

    Thanks in advance any new ideas would b great.
    Hi KTM,

    Hope you’ve got the bike to match the name
    Are you from the North or South? I’ll hazard a guess at the south.

    The R22 VRV Plus units are very difficult to understand with a service checker, it will only show you what the pcb is out putting and receiving from the sensors. You would need to judge if solenoid valves, reversing valves and expansion valves are operating correctly based on the thermistor readings.
    i.e. If the reversing valve is off (de-energised) the heat exchanger should be operating as a condenser & the heat exchanger header sensor should be similar to Tc (sat condensing temp)
    It will not automatically highlight a problem to you.

    Connecting the service checker directly into the function box pcb (not F1F2 terminals) will give a much faster update time.
    Last edited by VRVIII; 25-01-2011 at 07:44 PM.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin vrv seriously need help

    filters clean on indoors? grilles havent been blocked off to reduce airflow?
    check mode 41 for coil,return air,controller temp values.
    any bms interface or fault codes?

  8. #8
    gqm001's Avatar
    gqm001 Guest

    Re: Daikin vrv seriously need help

    On the newer units I have had a lot of problems with the outdoor thermistors losing their values but not showing as a fault, because of this the unit does not operate as epected.
    The other problem is installation of fresh air supply ducting being installed to close to the rear of a ducted unit when the ceiling void is used as plenum, sometimes the units will struggle to overcome the cold supply air. in this case if the return air sensor is in the indoor unit it will show that the system is working hard but without the expected performance.
    I expect that these are just things that we all would normally check but its always worth hereing other peoples views.

  9. #9
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Talking Re: Daikin vrv seriously need help

    Thanks for all the responses. Yea I was thinking we should check all the valves manually and not just listen to the service checker. The system never showed any fault. There is no BMs sytem only I touch. The only sensor that was reading off was one of the oil sensors which was replaced. I did think that fresh air on was too cold so the ahu were all turned off. This made no change to the system. I think I will try get back to site asap and go throughall the valves one by one.

    I do think it is a valve that is mechanically not operating correctly although it may be showing the correct pulses on service checker and not generating the fault. It's difficult to know were to start,
    Especially when u not working on the site.

    VRVIII I didn't know they made bikes
    Your correct on both accounts I'm from the south and I have 2 ktm bikes.

    Il keep u posted on what we find as soon as I can get back to site. Maybe the other engineer will have some more ideas 2m.

    Thanks again

  10. #10
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin vrv seriously need help

    Quote Originally Posted by ktm View Post
    System will run fine in cooling. Spoke to Daikin and replaced low pressure transducer.
    I would suggest you first check the calibration of the discharge pressure transducer (not the LP transducer) this has the main influence over compressor capacity in heating mode.

    It’s easier to check the calibration of all sensors before you start,
    Connect service checker
    Switch off all indoors at controllers and allow outdoor to stop
    Wait 30 min to allow pressures and pipe temps to equalise
    View checker to verify sensors are around the same value (discharge & oil pipe temps may be higher)


    Turn all indoors on in heating mode, when the system has been operating for 20~30min check the following at function unit and each module
    Ø Mode of operation – number of operating compressors
    Ø Head pressure – discharge temp – discharge superheat
    Ø Liquid line pressure
    Ø Suction pressure – suction temp – suction superheat

    Average indoor liquid, suction, air on & air off temps
    Last edited by VRVIII; 26-01-2011 at 11:26 PM.

  11. #11
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin vrv seriously need help

    Tanks for the ideas. I will try check these things when I get back to site next week. Thanks VRV III for getting back so soon great to have someone with a few new ideas. Il keep u posted.

  12. #12
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: Daikin vrv seriously need help

    Hi. Did you get to the bottom of this problem?
    In the words of David Byrne, Well...How did I get here?

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin assistance or LACK of it!!
    By brianocallaghan in forum Air Conditioning
    Replies: 7
    Last Post: 15-07-2010, 11:23 AM
  3. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •