    Iced Compressor and Twin Screw question...



    Hello Guys, i'm not new to air conditioning but i'm still a novice when it comes to troubleshooting. Can you please explain to me why did these pictures happen? And what are the probable causes and things to be done so these wont happen again...

    compressor




    suction line


    AHU




    Air Filter



    Also:

    My boss have overhauled a carrier 30GX screw compressor.. there were 2 identical compressors, one with a grounded winding and one with a mechanical problem...
    the one with a grounded winding was replaced with a winding from the other. When the compressor was started.. the compressor motor functioned but there was no compression... what could be the problem??

    many thanks to all..



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Iced Compressor and Twin Screw question...

    You are getting liquid back to the compressor. This could be caused by many things. It could be a bad TX valve, or a iced evap, or one of many other things. This will destroy the compressor if you do not sort it out.

  3. #3
    Join Date
    May 2001
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Iced Compressor and Twin Screw question...

    Switch it off and get a competant engineer to have a look at the system for you?

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Iced Compressor and Twin Screw question...

    Hi
    as said before you should have a ref look at the system ,you are working at either very low suction pressure due to lack of rerigerant,or low head pressure,or bad air flow over the coiles,and many other possible reasons,
    as for the screw ,it would seem like while assembling the comp either the slide valve wasnt placed correctly, or some other mechanichal issue.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Iced Compressor and Twin Screw question...

    The first thing to do is to get those coils cleaned, they look very dirty, then check the airflow.

    After that then you can check the refrigerant side.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2008
    Location
    Philippines
    Posts
    16
    Rep Power
    0

    Re: Iced Compressor and Twin Screw question...

    guys thanks for the answers.... you see im still new to this and still learning.. maybe some day i will be as good as you heheh
    cheers!

  7. #7
    Join Date
    Dec 2009
    Location
    England
    Age
    15
    Posts
    5
    Rep Power
    0

    Re: Iced Compressor and Twin Screw question...

    just for new guys reading old threads for hints...

    My first guess from these pictures would be blocked evaporator coil or more likely slipping belts on the evaporator. The maintenance appears poor so I certainly wouldnt rule out low running pressure, liquid flood back etc. Could be some clever sod altered the TXV adjuster!!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •